I’ve got a 2.6kw induction motor, inside the motor cap I’ve got 12 terminals, the machine it came off had a 2 speed setting, all the cables went back to a multipole switch for 1450 or 2800. I’m trying to use the motor from a single phase in 3 phase out VFD.
Tested the motor out and I seem to have 6 pairs all with about equal resistances, my question is 1 is it possible to run this motor delta for use on the VFD, 2 - how best can I identify which pairs I need to use to wire delta for use with my VFD
THANKS
I’ve got a 2.6kw induction motor, inside the motor cap I’ve got 12 terminals, the machine it came off had a 2 speed setting, all the cables went back to a multipole switch for 1450 or 2800. I’m trying to use the motor from a single phase in 3 phase out VFD.
Tested the motor out and I seem to have 6 pairs all with about equal resistances, my question is 1 is it possible to run this motor delta for use on the VFD, 2 - how best can I identify which pairs I need to use to wire delta for use with my VFD
THANKS
RE: Wiring to delta on 12 wire
A picture of the nameplate will get you a more accurate answer.
RE: Wiring to delta on 12 wire
RE: Wiring to delta on 12 wire
Is the motor still connected to the multi-pole switch? Find the 3 leads connected to the high speed terminals on the multi-pole switch. Those are the 3 leads you need to connect to your VFD.
RE: Wiring to delta on 12 wire
RE: Wiring to delta on 12 wire
RE: Wiring to delta on 12 wire
RE: Wiring to delta on 12 wire
To use it with a VFD, just connect it for the voltage that you are running at, the VFD will take care of the rest (with proper programming of course).
" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
RE: Wiring to delta on 12 wire
RE: Wiring to delta on 12 wire
RE: Wiring to delta on 12 wire
Delta is low speed (supply at 1U 1V 1W and 2U 2V 2W open).
Two Wye is high speed (supply at 2U 2V 2W and 1U 1V 1W shorted).
Tricky part is identifying the leads if they are not marked.
Muthu
www.edison.co.in
RE: Wiring to delta on 12 wire
Edison123 if I was to connect it in a fashion which I think is delta according to your diagram, if it was wrong would it not spin at all? I can try it on a true 3 phase supply as I’m dubious about connecting it to the VFD if I’ve got it wrong
RE: Wiring to delta on 12 wire
Muthu
www.edison.co.in
RE: Wiring to delta on 12 wire
Probably the motor has two independent windings and that the second nameplate is missing.
How to get more efficiency
RE: Wiring to delta on 12 wire
RE: Wiring to delta on 12 wire
Then you need to take it to a winding shop where they will most likely suggest to rewind it for your speed and connection since it a major pita to sort out 12 unmarked leads. Or buy a new motor for your specs.
Muthu
www.edison.co.in
RE: Wiring to delta on 12 wire
There is no way to tell if a motor is internally connected wye or delta from the supply wires. The inverter cannot tell a wye motor from a delta motor.
I once had to connect a consequent pole (Dahlander) motor with all the markings missing.
I removed the rotor and with a battery and a compass I identified each winding location and polarity by energizing a winding and then finding the physical location and polarity with the compass.
What is your supply voltage?
--------------------