Rafter-Wall Lateral, Shear and Uplift Resistance

Rafter-Wall Lateral, Shear and Uplift Resistance

Rafter-Wall Lateral, Shear and Uplift Resistance

(OP)
I have a question about designing the connection to Rafter - Wall.

We need to design the connections to resist lateral, shear and uplift, and if we are using a ridge board then we need to install nails for the rafter ceiling connection also to resist the thrust.

To resist lateral loads(perpendicular to wall) on the roof lets say I'm install a Simpson A35 Connector. And for the lateral loads parallel to wall, i need to install another tie. Lets say I'm installing a Simpson hurricane tie.

Is it ok to install two or more connections for a single place?

Can we install it practically and is there sufficient space for several connections?

or is there is another way to design it with a single connector?

RE: Rafter-Wall Lateral, Shear and Uplift Resistance

Is this a general question or are you looking at a particular connection with higher than usual loading?

A few comments:
1) Except for very tall walls or at jambs of large windows/doors, you're unlikely to have an out of plane loading that is more than what the typical face or toe nailing can handle. So your A35 should be a pretty rare item in this context.

2) Lateral load parallel to the wall should be transferred by blocking, not hurricane ties. Read the footnotes and fine print - they specifically say that they don't replace blocking for shear transfer.

3) You should still have hurricane ties, but you should be using them for uplift resistance and that's about it.

Other than that, a lot depends on the size of the stud and rafter. I'm not sure what the wood code is in your area, but here in the US we have the NDS. It gives rules for spacing of fasteners in connections, how a member can be loaded at a connection, etc. The individual pieces of hardware are great, but you have to apply engineering mechanics and the limitations set by your code to design them to fit and work together.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close