Lateral deflection of a pile with pilecap
3

Lateral deflection of a pile with pilecap

Lateral deflection of a pile with pilecap

(OP)
I was using the method in Tomlinson & Woodard publication to estimate the lateral deflection of a pile with a pilecap on top.

Firstly, I presume equation 6.21 applies, for a fixed head rather than a free head. I thought perhaps a fixed head may be for a pile within a pile group.

Has anyone seen empirical methods for calculating deflection if pilecap is semi submerged into the soil?

RE: Lateral deflection of a pile with pilecap

I think you have a free head condition with your single pile under a pile cap. There is nothing to provide frame action which would introduce the fixed head behavior.

I generally rely on the project's geotechnical engineer for the lateral analysis of the piles on my projects, but generally I have seen them use the bottom of the pile cap as the top of the pile for the purposes of L-Pile analysis. I think this would make the semi submerged portion of your pile cap not relevant in the lateral behavior of your pile. If you are considering your pile cap in your lateral analysis, I would think you could resolve this by considering just the submerged portion of the pile cap.

RE: Lateral deflection of a pile with pilecap

Quote (mte12

Firstly, I presume equation 6.21 applies, for a fixed head rather than a free head. I thought perhaps a fixed head may be for a pile within a pile group.)


- It is true that equation 6.21 is for deflection at head of fixed-headed pile..

- Fixed head may develop at a pile within a pile group with rigid pile cap but the pile would be deep and flexible .

Refer to Figure 6.30 ( Coefficients for calculating deflection of pile carrying both moment and lateral load )

Pls notice that Mt/(HT)= −0.93 for fixed-headed case and Mt/(HT)= 0 for free -headed case. You will see in-between cases where ,Mt/(HT) is (-0.1,-0.2,-0.3...-0.7..) as usual ..

RE: Lateral deflection of a pile with pilecap

(OP)
Thanks for advising.
I thought perhaps the ground would act as a fulcrum providing the fixed head, although I didn't really believe this due to assumption of an air gap from underside of pilecap to ground.
But it's not readily apparent in reading the text, the definition of free or fixed head.

EZBuilding, I agree that for a single pilecap, the pilecap being semi submerged, wouldn't make much of a difference to the deflection. But for a continuous pilecap, I thought it may be more significant. It's more of a question of what's normally accepted practice. Then again, the top portion seems to be ignored by some, in for example stability calculations.

If the pilecap is continuous along a single row of piles, I presume this is still a "free head" scenario. And for two rows of piles, this tends toward "fixed head".

HTURKAK, Figure 6.30 will be helpful actually.

Also, generally speaking, if a pile was modelled with springs (proportional to modulus of subgrade reaction), in your experience, would the deflection be similar, a bit less/more or significantly less/more?

RE: Lateral deflection of a pile with pilecap

Quote (Also, generally speaking, if a pile was modelled with springs (proportional to modulus of subgrade reaction), in your experience, would the deflection be similar, a bit less/more or significantly less/more?)


Then modell the pilecap ( together with the piles ) with FEM etc and see how fixity develops..

The left picture, free head at short dir. loading and fixed ( or probably partial fixity develops ) at long direction ..

RE: Lateral deflection of a pile with pilecap

This is my understanding on "fixed head" vs "free head" piles. I think Lpile can provide information on the deflection and slope of the shaft.



RE: Lateral deflection of a pile with pilecap

mte - I think the distinction for the load and deformation comes based on the modeling assumption. If the assumption is that the lateral load occurs at the top of the pile/bottom of the pile cap, then the soil above this load is not necessarily contributing to resisting it's load. It's also usually a beneficial assumption as the soil will tend to be stiffer as you get down from the top could of feet.

I align fixed head as a consideration that the pile and the pile cap are able to form "frame action" and transfer moments from one element to the other. In this condition, your modeling assumption would be similar to a fixed column and beam moment frame. The free head assumption would be similar to a cantilever column fixed at the base and free to rotate at the top. That capabilities for the fixed head condition to present itself would usually come about by having a second pile in the direction of the lateral loading which can become the second part of that frame action. In reality there may need to be some considerations for the relative stiffness of the piles and the pile caps in determining how much fixity you are getting - but I don't think that is typically considered in the geotechnical modeling of the fixed-head parameters.

RE: Lateral deflection of a pile with pilecap

(OP)
Thanks to all for the advice.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close