Radius of Gyration of a Noncomposite steel and concrete section
2

Radius of Gyration of a Noncomposite steel and concrete section

Radius of Gyration of a Noncomposite steel and concrete section

(OP)
Hello, when calculating the radius of gyration (for moment magnifiers based on KL/r) for a non-composite steel and concrete circular section would you use the hollow steel section's 'r' value? If so, why? Can you provide me some code or AISC reference for this?

When researching this, Table 4-13 of the AISC 14th edition shows a composite section radius of gyration to be equal to the hollow HSS sections 'r'. Unfortunately there's no non-composite circular section 'r' value given in these tables. Any help is appreciated.

RE: Radius of Gyration of a Noncomposite steel and concrete section

I guess no one is biting, but IIRC that is because the strength of the column should be designed as the sum of its components. If you have good reason to believe there is bond between the two (doubtful), you could use the modular ratio to calculate I and A values and you would get a modified r value.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Out of curiosity, I have to ask: why would you add both concrete and rebar into a steel CHS column and not account for composite action? There will be composite action (concrete is very strongly confined), and thus composite section stiffness (greater than only CHS stiffness) even if you decide not to calculate it.

RE: Radius of Gyration of a Noncomposite steel and concrete section

In Australian/New Zealand composite code, r is defined as follows for the gross section for use in determining the compression capacity (believe its the same in Eurocodes).



https://engineervsheep.com

RE: Radius of Gyration of a Noncomposite steel and concrete section

(OP)
@canwesteng
there is no reliable bond between the two, ultimately, the non-composite stiffness of the two is an average of the concrete and steel, so we brainstormed it in the office a bit more and realized that the program we're using calculates the moment magnifier based on the entire cross section and if we consider it a concrete section, per AASHTO LRFD the max KL/r is 100, if we only consider steel, max is 120. However a non-comp section is a grey area when it comes to finding the "r". Do we use the "r" for steel hollow section or the entire section? Using only steel gives us a larger "r" and therefore a KL/r of 115, but using the entire section yields a KL/r of 143. However, based on the maximum demand at the bent location, where these columns are located, we only need the steel sections flexural (and shear) capacity to resist the governing factored loads. Therefore, we've found it reasonable to ignore the concrete in these calculations and consider steel only. Adding concrete shouldn't make it worse for the structure.


@centondollar

That is a good question, initially it was for two reasons, one being added stiffness for drivabliity (so the hollow section won't plug with soils when driving it 80 feet) and to produce a partially fixed connection from column to bent (only a small cage developed into the cap) but based on my response above, we only need the moment capacity of the steel section (only partially developed into the bent cap) to handle the maximum factored forces from Strength and Service load cases.

@Agent666
Thank you for the composite equation, however I was curious if I can just ignore the concrete in calculating the KL/r in this non-composite situation, as that would give me a value less than 120, which per AASHTO is acceptable to have for a column.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Are you using Chapter I of the spec? It goes into depth on determining direct bond interaction for composite action in filled members, force allocation procedures, etc.

RE: Radius of Gyration of a Noncomposite steel and concrete section

(OP)
@phamENG

I'm not considering composite action between the concrete and steel, it's a 16" steel section, 1" thick that's 80 ft long, there's no feasible construction method to weld shear bolts all along it to make it behave like a composite section.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Right. There's also no feasible construction method to weld shear bolts along the length of the inside of a 6" pipe column, but that doesn't stop the SCM from listing composite section properties. That's because, in Chapter I, there's a set of equations that you can use to evaluate the effective bond between the steel and concrete in contact with one another. It's nowhere near as good as headed studs on, say, an encased composite member, and the phi/omega factors give some hints as to the variability of the effect, but it's there and can be relied upon. There's some info in the commentary.

If you really don't want to...then it also says that the column shouldn't be any weaker than the steel section without concrete fill.

RE: Radius of Gyration of a Noncomposite steel and concrete section

(OP)
Yeah currently we really don't need the concrete for any additional capacity, the 16" hollow steel section can handle the axial and flexure demands it's subjected to so as a stand alone model it should be able to handle the loads there. Thank you for that input on the commentary, if we need to sharpen our pencils I'll look at the commentary and see what additional capacity I can take from that interaction, it must all be skin friction contribution right?

RE: Radius of Gyration of a Noncomposite steel and concrete section

Quote (Who I Am)

it must all be skin friction contribution right?

Essentially. As centondollar mentioned above, the concrete is well confined and the friction between the two is sufficient to cause composite action.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Regarding composite behavior.

1) I'm pretty sure that, somewhere, AISC will let you do composite action for a wide flange beam with external concrete and no mechanical connection. So "bond" is certainly a real thing.

2) I'd certainly be hesitant to rely on bond for composite behavior in something that you intend to beat the heck out of during piling.

3) When it comes to resisting flexural demand, I've found interior concrete fill to be pretty ineffective. That, because:

a) Shrinkage within a long member pretty much guarantees that you have to assume the concrete to be cracked, even if the cracks are small and well distributed as one would hope.

b) Interior concrete, especially cracked interior concrete, doesn't operate at much of a flexural lever arm.

4) I'd be comfortable using the concrete for axial loads but:

a) You can probably do this without composite action anyhow.

b) Shrinkage and creep mean that your axial load will tend to migrate over to the steel anyhow.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Quote (KootK)

2) I'd certainly be hesitant to rely on bond for composite behavior in something that you intend to beat the heck out of during piling.

I've only done this once (maybe twice?), so I'm far from an expert, but we had bottom plates welded to the pile and drove it hollow. Then concrete was poured into the pile from a barge. Seemed to work out pretty well.

RE: Radius of Gyration of a Noncomposite steel and concrete section

I've been noodling on the kL/r issue for a few days now. In the process, I've realized that my understanding of the nature of those checks has been pretty superficial. Yes, it's a check against "slenderness" but what exactly does that mean and how do you extend that to a non-conventional situation? Here's what I think kL/r means based on the derivation of the equations that we use:

1) You want a member not excessively prone to P-baby-delta moment amplification under axial load.

2) Since apparent flexural stiffness approaches zero as the axial load approaches the Euler buckling load, achieving #1 means controlling the ratio of the applied load to the Euler buckling load.

3) To simplify matters for #2, we do the kL/r check without involving the applied axial load. To manage that, we instead assume that the designer intends that the member will achieve some, reasonable ratio of it's squash load (As x Fy, Ag x f'c). Whether that ratio is 0.3, 0.5, or 0.7, I don't actually know.

4) In conclusion, [kL/r < WHATEVER] is a comparison between the Euler buckling load and the squash load of the member. I feel that the important takeaway from this is that the Euler load and the squash load are calibrated to be associated with:

a) The same cross section.

b) materials having the same stiffness.

c) Materials having the same max stress (Fy, f'c).

So, applying this to OP's practical question, here's what I come up with:

A) If OP's steel section is designed to deal with 100% of the moment and axial load, then kL/r < 120 is surely appropriate.

B) If it will be the concrete taking some or all of the axial load then kL/120 will still be appropriate so long as the total axial load does not exceed the squash load of the steel section. That, because in this situation, the steel section alone is still stiff enough against lateral movement that it is capable of stabilizing this amount of axial load whether it resides in the steel or the concrete.

C) If the concrete will take some of the load, and that load is greater than the squash load of the steel section, then kL/r < 120 is no longer appropriate. That, because in this situation, the steel section alone is not stiff enough against lateral movement that it is capable of stabilizing this amount of axial load.


RE: Radius of Gyration of a Noncomposite steel and concrete section

(OP)
Thank you KootK, this falls within the A) scenario, and it is drivable so no squash load (i like that term). I believe that this design is okay because you're judgement is similar to our understanding. Thank you all for your contributions.

RE: Radius of Gyration of a Noncomposite steel and concrete section

I'm not familiar with the US code references, but moment magnification/amplification becomes less accurate as the second order effects increase. One measure of this is the magnitude of the amplification factor which takes account of the load as well as slenderness. Another measure is the raw slenderness which gives a measure of sensitivity of the results.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Quote (KootK)

4) In conclusion, [kL/r < WHATEVER] is a comparison between the Euler buckling load and the squash load of the member.

Not sure if already considered in the noodling, but column curves tend to lie slightly above:

N_squash/[1 + (N_squash/N_Euler)]

The weakest Australian steel compression curve (highest residual stress) follows this closely (within ~2% over the full range), while the other four are above it (and quite considerably in the inelastic region for the strongest couple of curves). But the trend is there. Similar for aluminium compression and steel bending, where that equation gets up to ~20% conservative at the worst match.

So, while concrete design doesn't use the column curve, this should give an estimate of where kL/r=100 lies in terms of capacity relative to squash load.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Check out this AISC Publication Concrete Filled HSS.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Quote (steveh49)

Not sure if already considered in the noodling

No, I'd not considered that at all. Thanks for sharing your observations.

Quote (steveh49)

Another measure is the raw slenderness which gives a measure of sensitivity of the results.

Can you elaborate on what you mean by "raw slenderness"? I get the impression that you see that as a load independent slenderness. Presently, I'm of a mind that there's really no such thing. Further to that, this has me wondering if there's a justifiable way to cheat these slenderness ratios. Consider:

1) kL/r = 120; the 120 is really [SQRT(E/Fy) x MARGIN]. This is a squash load comparison.

2) If I want to sharpen my pencil, could I sub in the real axial stress as [SQRT(E/Fa) x MARGIN]. This is a slenderness comparison based on the real load.

In this way I feel as though one could say that they have a kL/r > 120 but still satisfy the requirement if kL/r < SQRT(E/Fa) x MARGIN].

Congratulations on being the Eng-Tips Grand Wizard last week! For seven days and seven nights, your word is law.

RE: Radius of Gyration of a Noncomposite steel and concrete section

I meant kL/r when I said raw slenderness. Moment magnification is mentioned as the reason for the question being raised and I came from the Australian perspective where the kL/r=120 limit in our code (compared with AASHTO's 100) is just a limit on the moment magnifier method. We can push past if we do a higher-tier analysis. So I suspect the same applies to the AASHTO code, but don't know for sure. That would rule out cheating based on structural behaviour as it's the simplified analysis method that is being limited.

In terms of where the limit sits between 100 & 120, I'd be happy with a sliding scale based on relative contribution of EcIc & EsIs to the total EI.

Correct me if wrong, but ACI 318 doesn't have the kL/r limit, just the limit on second order effects compared to linear effects? That seems to be similar to how you would want to 'cheat' AASHTO.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Regarding ACI limits, I found this article which might be helpful.

American Concrete Institute (ACI) [..] defines the criteria for the effect of slenderness ratio. The slenderness ratio can be neglected for compression members braced against sideways when


RE: Radius of Gyration of a Noncomposite steel and concrete section

Quote (steveh49)

Correct me if wrong, but ACI 318 doesn't have the kL/r limit, just the limit on second order effects compared to linear effects? That seems to be similar to how you would want to 'cheat' AASHTO.

Yes, that's how see the 318 situation as well.

Quote (steveh49)

Moment magnification is mentioned as the reason for the question being raised and I came from the Australian perspective where the kL/r=120 limit in our code (compared with AASHTO's 100) is just a limit on the moment magnifier method. We can push past if we do a higher-tier analysis. So I suspect the same applies to the AASHTO code, but don't know for sure. That would rule out cheating based on structural behaviour as it's the simplified analysis method that is being limited.

I'm not sure that I agree that it would rule out "cheating" in this instance. If the simplified method is limited because it becomes inaccurate as the axial load approaches the Euler load, then this too should be something that could be addressed by way of comparison to the actual axial load rather than the squash load.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Quote (steveh49)

I'm not familiar with the US code references, but moment magnification/amplification becomes less accurate as the second order effects increase.

I'm also curious to know what informs your opinion on that. My understanding of our conventional moment amplification setup is that it is based on a truncation of an infinite series. As P/Pcr approaches unity, the truncated terms of that series become less "neglectable". So there's that. Do you know of more?

RE: Radius of Gyration of a Noncomposite steel and concrete section

Nawy mentions it, but I was actually mis-remembering the second image. The problem isn't caused by the magnifier per se, but the inaccurate moment-curvature relationship that goes hand in hand with it. Good to be forced to brush up occasionally.






In terms of cheating, it depends on what the rules are. If structural adequacy is the only constraint, a purely geometric limit has no validity (unless the column is so tall the self-weight exceeds strength, I suppose).

If it's compliance with a rigid code limit on geometry, no cheating.

If you have something like the Australian code, you might judge that a column would pass the rigorous analysis without actually doing it, based on utilisation calculated from the moment magnifier despite using it beyond its code limit. But, in the bridge world in my area, such a slender column would be subject to independent review, and the reviewer might call your bluff.



RE: Radius of Gyration of a Noncomposite steel and concrete section

The true property of a "non-composite" concrete-filled pipe column can only be established by testing. It is conservative yet reasonably accurate to use the "r" value for the steel pipe only when the column is subjected to bending.

RE: Radius of Gyration of a Noncomposite steel and concrete section

Quote:

We can push past if we do a higher-tier analysis. So I suspect the same applies to the AASHTO code, but don't know for sure.

That's correct. A higher-tier analysis, considering P-delta effects is required by AASHTO if the range of applicability for moment magnification is exceeded. The lower limit for AASHTO could be for efficiency. When columns get to be that slender, there are usually boundary conditions (limits on displacements due to the connection to the bridge superstructure) that limit the moment.

There's also that the length to fixity is typically dependent on soil properties, which are highly variable, so defining the unbraced length cannot be done with any great degree of accuracy.

Rod Smith, P.E., The artist formerly known as HotRod10

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close