MCC Bus and Incomer Breaker Sizing

MCC Bus and Incomer Breaker Sizing

MCC Bus and Incomer Breaker Sizing

(OP)
Can we calculate the load current for Sizing the Busbar and incomer breaker with Motor Shaft power? Process and Mechanical Team have given us the motor Shaft power. Can I use this data instead of the Rated Power of the motor to calculate the Current and size of the Breaker? Please advise.

RE: MCC Bus and Incomer Breaker Sizing

Dear Mr. Histor (Electrical)(OP)16 Mar 22 10:51
" Can we calculate the load current for Sizing the Busbar and incomer breaker with Motor Shaft power? Process and Mechanical Team have given us the motor Shaft power. Can I use this data instead of the Rated Power of the motor to calculate the Current and size of the Breaker? Please advise."
1. No. " Motor Shaft power " is the motor [output power] needed in (kW) to drive the mechanical load.
2. The [electrical input] to the motor in (kVA) > Motor Shaft power in (kW). This is due to the (power-factor) and (efficiency) of any motor are always < 1. e.g. pf=0.8 and eff=0.9...
3. If the breaker and busbar is supplying only one motor, is shall be at least sized to say >1.25 of the calculated kVA. Refer to local regulation which may differ depending on IEC or NEC applicable at the location.
4. However, if the breaker and busbar is supplying [a group of motors], they can be < than the total [sum of the Motor Shaft power] in (kW). This is taking into consideration that NOT all the motors are loaded continuously to the maximum (kW) at the same time. Refer to local regulation which may differ depending on IEC or NEC applicable at the location.
Che Kuan Yau (Singapore)

RE: MCC Bus and Incomer Breaker Sizing

(OP)
Dear Mr. Kuan Yu, For Example there are 3 Motors connected to an MCC.

Motor A : Rated power 3kW, Shaft Power 2.6kW
Motor B : Rated power 15kW, Shaft Power 12.8kW
Motor C : Rated power 37kW, Shaft Power 32.8kW
All motors are on continuous duty. 400V, 0.85 PF

in This case for Sizing the MCC Bus and Shaft Power, Can I use Shaft power (Actual required power) for Calculation Circuit overall current and Size the Circuit Breaker?

Procedure 1: Sizing the Circuit Breaker using Shaft Power
Overall Shaft power = 48.2kW
Load Current = (48.2x1000)/ (1.732x400x0.85) = 81.8A
Size of Circuit Breaker = 1.25 x 81.8A = 102.25AT / 160AF

Procedure 2: Sizing the Circuit Breaker using Rated Power
Overall Rated power = 55kW
Load Current = (55x1000)/ (1.732x400x0.85) = 93.4A
Size of Circuit Breaker = 1.25 x 93.4A = 116.75AT / 160AF

I have been doing Procedure 2. But some of my colleagues told me to follow Procedure 1. Please advise if I can use Procedure 1?
in the given example the number of loads is less. But in reality, we have more loads so I get a significant amount of difference in Load Current when I use these two Procedures.

RE: MCC Bus and Incomer Breaker Sizing

Dear Mr. Histor (Electrical)(OP)
"....#1. I have been doing Procedure 2. But some of my colleagues told me to follow Procedure 1. Please advise if I can use Procedure 1? .... #2....in the given example the number of loads is less. But in reality, we have more loads so I get a significant amount of difference in Load Current when I use these two Procedures...."
#1. Your procedure 1 is based on "overall Shaft power" and arrived at [load current] 81.8A with pf=0.85 is incomplete. You have to consider the efficiency factor say (0.9 ?). See my post dated 17th instant Your procedure 2 is based on "Overall Rated power" and arrived at [load current] 93.4A with pf=0.85 is also incomplete. You have to consider the efficiency factor say (0.9 ?). See my post dated 17th instant.
# 2. In reality a MCC would have more loads. You have to refer to the [local regulation/law] which differ; depending on IEC or NEC that is applicable at the location.
Che Kuan Yau (Singapore)

RE: MCC Bus and Incomer Breaker Sizing

(OP)
Dear Mr. Kuan Yu,
Thanks for your reply. What I want to understand is, Can use Shaft power for sizing incoming breakers? I mean the consumed power = Shaft power/efficiency Can I use this consumed power of a number of loads for calculating the incomer breaker current? or do I need to use the rated power of the motors to calculate the current? Thanks.

RE: MCC Bus and Incomer Breaker Sizing

Dear Mr. Histor (Electrical)(OP)21 Mar 22 08:59
".... What I want to understand is, Can use Shaft power for sizing incoming breakers? I mean the consumed power = Shaft power/efficiency Can I use this consumed power of a number of loads for calculating the incomer breaker current? or do I need to use the rated power of the motors to calculate the current? ...."
1. Your [ consumed power]* is the [ mechanical load power in (kW) at 100% loading].
2. Your [ rated power of the motor in (kW) ]** is > [ consumed power]. This is the usual case taking possible "short time over-load" into consideration or that is the next higher standard kW size.
3. Based on above [ ]* and [ ]** ; the breaker and busbar shall be based on [ ]** i.e. taking care of possible over-loading.
4. Attention: The breaker and busbar may be < sum of all [ ]** . You have to refer to the [local regulation/law] which differ; depending on IEC or NEC that is applicable at the location.
Che Kuan Yau (Singapore)

RE: MCC Bus and Incomer Breaker Sizing

No, you can not size power wire or bus that way. You must use the rated power. Generally, using 125% of largest motor plus all the other motors is the smallest you should use. Also generally, you use the ANSI or NEC or UL rated motor current tables as the minimum motor current.

The breaker could be whatever you want, there is only a maximum on that. Go too small though and you won't be able to start the motors or will get trips randomly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close