Dear Mr. Kuan Yu, For Example there are 3 Motors connected to an MCC.
Motor A : Rated power 3kW, Shaft Power 2.6kW
Motor B : Rated power 15kW, Shaft Power 12.8kW
Motor C : Rated power 37kW, Shaft Power 32.8kW
All motors are on continuous duty. 400V, 0.85 PF
in This case for Sizing the MCC Bus and Shaft Power, Can I use Shaft power (Actual required power) for Calculation Circuit overall current and Size the Circuit Breaker?
Procedure 1: Sizing the Circuit Breaker using Shaft Power
Overall Shaft power = 48.2kW
Load Current = (48.2x1000)/ (1.732x400x0.85) = 81.8A
Size of Circuit Breaker = 1.25 x 81.8A = 102.25AT / 160AF
Procedure 2: Sizing the Circuit Breaker using Rated Power
Overall Rated power = 55kW
Load Current = (55x1000)/ (1.732x400x0.85) = 93.4A
Size of Circuit Breaker = 1.25 x 93.4A = 116.75AT / 160AF
I have been doing Procedure 2. But some of my colleagues told me to follow Procedure 1. Please advise if I can use Procedure 1?
in the given example the number of loads is less. But in reality, we have more loads so I get a significant amount of difference in Load Current when I use these two Procedures.