How to set wind load if my country standard is not added to the load pattern?
Can I use it for ASCE 7-...?
Can I use it for ASCE 7-...?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Contact USThanks. We have received your request and will respond promptly. Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting Guidelines |
|
Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.
Here's Why Members Love Eng-Tips Forums:
Register now while it's still free!
Already a member? Close this window and log in.
RE: How set wind load manual
You'll probably need to do this the old-fashioned way. Define a master node for each level at the location of the wind load resultant. Define a rigid diaphragm for each level. Compute the wind load resultants and apply them at these master nodes.