Stress Corrosion Cracking and HE to tensioned high strength 7-wire carbon steel strands

Stress Corrosion Cracking and HE to tensioned high strength 7-wire carbon steel strands

Stress Corrosion Cracking and HE to tensioned high strength 7-wire carbon steel strands

(OP)
I recently extracted 4 failed 7-wire steel strands from a post-tensioned concrete parking/plaza deck.

Strand tendons are the typical MUTS 270 ksi, 1/2" diameter, greased and sheathed, and the structure is 20 years old, and otherwise in excellent condition with meticulous maintenance etc. The strand tendons are typically under a tensile stress of approx. 70% of MUTS.

At each of four locations there was about 8" of strand tail that exited the building slab edge, so we extracted the strands to determine probable cause.

We have done this many, many times, with often the reason for failure is due to someone installing post-installed fasteners (rotary-percussion drilling), but for older structures (>30 years old) it is often corrosion related, usually significant pitting over several feet of strand in close proximity to the failure location.

But with the 4 extracted strands to this project the corrosion was very localized (less than 12" length), and whilst there was the characteristic pitting, some of the wires with brittle fracture have what looks like longitudinal cracking along the length of the wire over about 5 wires diameters.

Is it possible to identify stress corrosion cracking and/or hydrogen embrittlement based off visual review, or is full metallurgical testing/analysis required?

Here are some sample photographs. I partially uncoiled the 6 outer wires to show the damage across all wires.





I am assuming that HE is less likely, unless environmental hydrogen caused the embrittlement, but that would require a breach through the tendon sheath AND a breach through the slab waterproofing too.

Thanks for your input.


RE: Stress Corrosion Cracking and HE to tensioned high strength 7-wire carbon steel strands

Were these strands under any possible cyclic loading? So they may have failed under fatigue?
If there is no sign of water ingress, how can corrosion have occurred?

* Finding a solution is great * Knowing how to implement it is fantastic * Believing it is the only one and best is naive ?

RE: Stress Corrosion Cracking and HE to tensioned high strength 7-wire carbon steel strands

I have seen the long breaks in spring before. Usually the combination of prior surface damage and HE (from localized corrosion).
That you had multiple failures so close together makes me suspect that the damage happened after the cable was manufactured.
Such as in handling or installation.
You need some lab work on this.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed

RE: Stress Corrosion Cracking and HE to tensioned high strength 7-wire carbon steel strands

(OP)
Thanks Ben and Ed for the replies.

There is no fatigue of significance - one of the benefits of prestressing steel in prestressed concrete - under cyclic applied loads to the slabs does not change the tensile force in the strands by any magnitude.

There are however, changes in slope/angle of the tendons along their length - they are placed in parabolic profiles along the slab spans - although the angle changes are very small in this case.

There had to have been a local breach in the concrete and protective sheath to the strand for corrosion to have taken place - we just have to find it.

We shall get the failed segments to a lab and get some microscopic/metallurgical analysis done.

Thank you.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close