Diesel fuel piping?

Diesel fuel piping?

Diesel fuel piping?

(OP)
I am installing a day-tank for a diesel generator.  What type of piping should be used between the day-tank and the main diesel tank?  
 
Thanks in advance.
Replies continue below

Recommended for you

RE: Diesel fuel piping?

Need more info to help you.  Is this a small generator set with rubber mount? (Threaded pipe with flex hose to engine’s fuel filter).   It is best to follow the manufacture’s recommendations.  Get the generators installation manual and follow there recommendations.

Do not use any galvanized pipe.  Zinc will leach into the fuel and cause injector problems.

RE: Diesel fuel piping?

Also be sure to check out the fire protection codes

Patricia Lougheed

Please see FAQ731-376 for tips on how to make the best use of the Eng-Tips Forums.

RE: Diesel fuel piping?

(OP)
The generator manufacturer advises using "black iron pipe" through out the diesel fuel system.  I have been informed to definitely keep away from galvanized and copper conduit.

What is "black iron pipe?" and what protection does it need if it is going to be buried in the ground?  Can "black iron pipe" be purchased with an anti-corrosion coating?

Thanks,

RE: Diesel fuel piping?

No such thing as "black iron pipe". There used to be wrought iron pipe, but it hasn't been manufacturered or available in several decades. They likely mean carbon steel pipe, like A53F (very often junk - I'd avoid it), A53B ERW, or A106B seamless.

Check the code requirements for fuels in your area. If you're going to bury a fuel line, I'd bet you have to meet the same standard as the gas station operators.

RE: Diesel fuel piping?

in addition to that line,it will be better to provide a level controller or indicator.

RE: Diesel fuel piping?

1) In the field, black iron pipe commonly refers to carbon steel pipe such as A53, A106, A120 etc. without a galvanized, painted, or tape coating.
2)  Typically it is socket welded sch 80 for 2 inch and smaller.  Hook ups to the generator should be an approved flexible hose, as opposed to hard piped.
3)  Buried fuel piping is typically installed in double containment piping.  The project I did used 1 inch carbon steel piping contained inside a 3 inch fiberglass containment piping system.  

RE: Diesel fuel piping?

Onan/Cummins (Emergency Generator) Application manual requires black steel pipe for diesel fuel lines - Do not use galvanized fuel lines, fittings or tanks. Condensation in the tank and lines combine with sulfur in the fuel to produce sulfuric acid. The sulfuric acid reacts with zinc in the galvanized coating and contaminates the fuel. Do not use copper tubing for diesel fuel lines. Diesel fuel polymerizes (thickens) in copper tubing during long periods of standby and will clog the fuel injectors. Use a flexible section of tubing (code approved) between the engine and fuel supply line to withstand generator set vibration. The manual shows figures (12 & 13) for day tank piping depending on if main supply tank is below or above the generator. So get the application manual.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close