Gas Regulator Vent Termination Locations

Gas Regulator Vent Termination Locations

Gas Regulator Vent Termination Locations

(OP)
Hello,

Does anyone have experience with or know of code in NFPA 54 or IFGC that states required distance for gas regulator vent terminations above grade? Want to terminate these through side wall on first level of the building.

I can't find anything in these codes. Also, anything on distances operable windows or doors?

Thanks for any help

RE: Gas Regulator Vent Termination Locations

Best thing to do is to consult with your locality fire department or the state fire marshal.

RE: Gas Regulator Vent Termination Locations

Also consult the manufacturer or the distributor of the gas regulator. The instruction that comes in the packaging may alsogive you additional information.

RE: Gas Regulator Vent Termination Locations

Contact the local gas utility for guidance.

An example is National Grid Gas operating in NY, RI, and MA which shows these clearances:

NGG

The local building code official should also have this information.

RE: Gas Regulator Vent Termination Locations

I generally use the diagram in the IFGC Appendix C for discharge vents from appliances. Also, be careful of air intakes complying with ASHRAE 62.1

RE: Gas Regulator Vent Termination Locations

You might also take a look at the Plumbing Code and mirroring the rules for a sanitary vent. They are surprisingly similar. If it is a large diameter/high flow though, you'll want more clearance than the minimums.

RE: Gas Regulator Vent Termination Locations

This provides some guidance https://inspectapedia.com/plumbing/Gas_Meter_Clear..., but check your building code, or you will have trouble with your AHJ. The link includes a bunch of references, at the end.

Part of the answer depends on the type and size of the regulator, some regulators include a pressure relief function. It also makes a difference if this is a utility owned regulator or customer equipment.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now
The Great Project Profitability Debate
A/E firms have a great opportunity to lead the world into the future, but the industry’s greatest asset—real-time data—is sitting wasted in clunky, archaic ERP platforms. Learn how real-time, fully interactive dashboards in a modern ERP allow you to unlock data that will shape the future of the world. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close