Concrete strength for a lifting point
2

Concrete strength for a lifting point

Concrete strength for a lifting point

(OP)
Hello, I work in a small R&D lab. Our CTO had our technician set up a lifting point using a concrete beam in the ceiling of our lab (a week when I was out). I would like to validate the strength of this setup to make sure it is safe, since it was done very ad-hoc.

The setup is a 3/4"-10 double threaded stud through an existing ~3/4" conduit sleeve in a concrete beam. The beam's dimensions are 12" in height and 12" in width. The sleeve is 8" from the bottom of the beam. The two ends of the stud are nutted + pinned, and are used to hang chain for a chainfall.

I have done a hand calculation for the stud (125 ksi min tensile strength) assuming two-point beam bending. Using a factor of safety of 5, I found it to have a 700 lb capacity (350 lb vertical load per side).

My question is: how can I validate the strength of the concrete / what should I consider for that analysis? I do not have a lot of experience with concrete analysis, so I would appreciate any insight or references. I do not have access to any of the building plans or technical information. I would also appreciate feedback if it is a bad idea to even try to do a validation for this - I am just trying to do due diligence one way or the other.

Some folks in the office already lifted 600 lb with the setup (again, I was not involved when they did). If we do decide on an actual load capacity, we will test it at 125%.

Thank you
Mike

RE: Concrete strength for a lifting point

So the setup looks something like the following?




If so, and assuming the span is not excessive, applied load is relatively small in magnitude and short-term only, then you probably do not need to consider span-type 'global' effects.

You need to check the 'local' concrete failure modes like direct-tension pullout of the existing conduit (possibly a form tie hole?) with through-bolt/stud. Without knowing the existing rebar within the beam, you will either 1] have to assume an unreinforced section or 2} GPR span the beam and determine shear stirrup spacing and longitudinal rebar, and possibly probe the beam to check for rebar diameter.

For direct-tension, if you assumed a 45o failure-plane (actual will be be more like 35o to horizontal) that would give you a failure area of 1.414 *8" * 12" beam width x 2 sides = 271 in2. Assuming a concrete tensile strength of 200 psi (this would need to be verified and also check beam condition for existing concrete cracking in proximity to the connection) and that would give you a pullout strength of 54,000 lb.f

With a through-bolt at failure you will have curvature of the bolt/stud and local high-contact bearing stresses under the invert of the conduit/concrete way before 54 kips.

Seems you will be limited by bolt/stud capacity, or maybe chain capacity depending on the chain size/grade.




RE: Concrete strength for a lifting point

I agree with Ingenuity regarding checking a simply wedge type failure. Seems you have lots of concrete capacity regarding pull out.

As far as global failure, you are adding to the live load of the floor over. I wouldn't really want someone hanging ~1000 lbs beneath my floor without assessing it.

RE: Concrete strength for a lifting point

I would not want to put a 54K load on that beam... the beam will fail.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: Concrete strength for a lifting point

It’d be some chain block! bigsmile

RE: Concrete strength for a lifting point

I was thinking that there should be a bit of a disclaimer to the effect that failure of the beam may occur long before the load of that magnitude could be applied...

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: Concrete strength for a lifting point

I would have thought the issue is more that if the bolt bends even a little then you can get some local cracking / crushing of the concrete at the shoulders of the hole?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Concrete strength for a lifting point

With that load, a few things could go wrong...

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: Concrete strength for a lifting point

(OP)
Thank you Ingenuity for the helpful post (your diagram does represent our situation), I appreciate your time, and everyone else for your advice. This helps a lot with our assessment.

RE: Concrete strength for a lifting point

(OP)
One more question - there are two lifting points that have been set up. The concrete condition in the first is very good, no indications. In the second, near the form ties, there is some missing material (much of which has been painted, so it has been that way for some time). This is more of a basic statics question: for static loads, do irregularities in the surface "de-rate" the static capacity of the member, i.e. act as stress concentrations? As far as I can tell, there is no crack propagation through the bulk material. I know for structural steel, stress concentrations are less relevant, but I am wondering if it is more relevant for concrete as a brittle material.


RE: Concrete strength for a lifting point

Usually the hanger is a stirrup, this will fit close to the beam and minimize the bending of the bolt.
The bolts should be close fitting in the holes also. We used double ended studs so that the center portion was smooth, no bending of threads.
Then make sure that the hoist is small enough. Stencil the max lift on concrete and make it clear that they cannot use a larger hoist.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed

RE: Concrete strength for a lifting point

I'd probably use a BAR 1/4x3 and bend it so it slips over the beam just to minimise bending in the pin. Your advice to paint the capacity on the beam is excellent.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik

RE: Concrete strength for a lifting point

I agree that bending of the bolt is your main concern after seeing the photo. The localized spalling of the concrete around the exposed portion of the through-bolt is not so much an issue for the concrete beam as it effectively increases the "cantilever" length of the bolt as the point of fixity or fulcrum gets shifted back further into the web of the concrete beam thus increasing the stress on the bolt. You can eliminate or lessen the bending of the bolt and just rely on direct shear of the bolt by placing your bearing point as close to the face of the concrete beam web as possible. As dik mentioned, perhaps with some bar or angle iron.

RE: Concrete strength for a lifting point

(OP)
Thank you STrctPono for the input. I agree with your concern. When I did my nominal stress analysis on the bolt, I assumed a cantilever length of 2" to be conservative, which I think is about 0.75" longer than the apparent length.

The steel strap is definitely an interesting idea.

RE: Concrete strength for a lifting point

(OP)
I did a global analysis on the overall concrete beam for simple bending. I got a tensile bending stress value of 117 psi. I have to admit my own ignorance (my career so far has mostly involved metal...), I am not sure what to do with that. Based on Ingenuity's post, a conservative assumption for the tensile stress of un-reinforced concrete is 200 psi. I guess that only gives me a safety factor of ~1.7? Ignoring, of course, all the other loads on the beam. I am honestly surprised, I did not expect a 700lb load to be that significant.

RE: Concrete strength for a lifting point

That’s not how you assess concrete bending strength. Concrete is assumed to have zero tensile strength for bending purposes, and is indeed generally cracked at services loads (Eg cracked at midspan), which is where tensile reinforcement comes in.

For anchorage pullout you do rely on the tensile forces in the concrete, to resist a chunk of concrete tearing out.

RE: Concrete strength for a lifting point

toothless48,

We don't run stress checks like you would for an isotopic metal in conventionally reinforced concrete... at least not to verify Limit State Design. Any chance you can get your hands on the as-built drawings for your building? There really will be no other way to verify the existing reinforcing steel in the member. You would also need span length, weight of concrete beam and any tributary elements framing into it.

RE: Concrete strength for a lifting point

(OP)
Tomfh/STrctPono, thank you, I appreciate the advice. I seem to have found myself slightly out of my depth with this one. I will try to see if the building plans are available, although the building is quite old - at least part of the building was built in 1903.

RE: Concrete strength for a lifting point

Quote (toothless48)

I am honestly surprised, I did not expect a 700lb load to be that significant.

I very much doubt that a single 700 lb applied (temporary?) load will be problem - it is basically equivalent to two or three large people in very close proximity, or a steel filing cabinet full of paper files (if such things exist in today's all-digital world).

You stated that you don't have the existing drawings, so I see two immediate options:

OPTION 1:

Visually check the existing beams for any pre-existing distress: excessive cracking, deflection etc. IF all checks out continue as follows:

Measure the existing span/s;
Measure the distance to any parallel/adjacent beams (so as to determine the tributary area as STrctPono stated);
Measure slab thickness;
Measure beam width and overall beam depth.

With above data, calculate the existing dead loads. For example: 20' span beam, 18" o/a depth x 12" wide beams @ 10' centers, with 6" thick slab will yield an existing DL (self weight) of 18,000 lb.f

If the proposed added NEW load is less than 5% of applied DL (900 lb.f in this example compared to new applied load of 700 lb.f) then you are ok.


OPTION 2:

If OPTION 1 does not check out, OR, if this is a 'mission-critical application' then probe and GPR scan the beam and determine existing rebar diameter and spacing, then calculate the flexural and shear capacities and compare to applied actions.

RE: Concrete strength for a lifting point

Quote (toothless48)

...although the building is quite old - at least part of the building was built in 1903.

Well then, 'step' carefully.

Under OPTION 2 you may need to consider materials sampling to check rebar grades, concrete properties.

What is the occupancy of the overhead beam/slab to which you have the hanging load attached? A roof, or an occupied floor?

RE: Concrete strength for a lifting point

I really don't think the beam is in any danger from a ~300kg load, but that's relatively easy to show.

The issue for me is the horrible connection "design" of the chain attachment.

There are a whole host of things going on here with forces in all sorts of directions. Can you give us a whole picture of the set up or draw it?

Inginuity drew it as hanging equally from both sides, but your description is rather vague. Do they hang straight down or connect to a single block? Do they just lift something up vertically then lower it down again?

Chains really need an end connection to properly form around the end chain link. Like the red links in this photo. And the design by StrcrPono above.



Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Concrete strength for a lifting point

(OP)
Ingenuity - thanks again for the detailed response. For "option 1", could you confirm how you calculated the 18,000 lbf dead load? I assume it is the beam weight + slab weight, using a typical concrete density. I've included a quick sketch of the beam geometry - would the tributary area be the beam span x the beam spacing, or is it decreased due to the contribution of perpendicular members taking some of the load?

To answer your previous question, the space above the beam is an occupied floor.



LittleInch - I appreciate the feedback. The two chains connect to a single chain hoist. Due to the geometry of the beam and the size of the chains, the beam spreads the chains, so the chains hang vertically next to the beam.

RE: Concrete strength for a lifting point

toothless48:

For the example I gave - assumed to be what we call a one-way beam-and-slab system - it is simply the cross-sectional area of concrete (in ft2) over the 10' assumed width x span length, so SW = [10' x 6"/12 slab + (12"/12 beam web depth) x (12"/12 beam width)] x 20' x 150 lb/ft3 = 18,000 lb.f

For your actual case with perpendicular beams the tributary area gets reduced slightly, as follows:



RE: Concrete strength for a lifting point

Toothless48:
You either want to get the stud/bolt threads out of the high shear and bending regions or you have to account for a significant reduction in shear and bending cap’y. because of the threads. Your photo shows that the bolt will suffer a significant bending problem because of the broken out hole at the face of the conc. beam. That would normally be the bolt bearing region, although the conc. bearing stresses would be very high. If I were doing this, I would make two steel plates, maybe .75” thk., by 8” wide, by about 20” long (vert. direction). That is about 2” above the bolt, 8” to the bot. of the conc. beam, plus 10” below the beam. These stl. pls. would be bolted tight to the sides conc. beam, by you existing bolt. Then, at the bot. of the stl. pls. provide drilled holes for two shackles, or cut pear shaped holes for a chain hook. My stl. pl. sizes are for design concept only, you design the pls. for your loads, and check your thru bolt cap’y.

RE: Concrete strength for a lifting point

In my opinion a steel trapeze would be unnecessary for 700 lbs.

I’d grout fill the voids, then use a rated eye nut plus plate washer on each side, then connect the chains to the eyes with rated shackles.

RE: Concrete strength for a lifting point

I'm with dhengr here. If 300kg fell off on top my foot I wouldn't be calling it a small load.

I would remove your bolt, repair the ends of the hole, use a solid bar for the majority of the beam width with enough threads left to tighten onto the steel plates and then attach your chains. You may want to add a cross bar between the two plates under the bean to reduce any bending moment on the plates or axial force on the bolt.

Then paint it yellow and make it look professional. What you have there would not pass inspection by any sort of certifying body or any client would see it and think these guys are cowboys...

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close