Fractionator feed furnace multiple passes

Fractionator feed furnace multiple passes

Fractionator feed furnace multiple passes

(OP)
Any one has idea how to to control Fractionator feed furnace multiple passes (8 passes)how to commissioning the flow during start up ?
Replies continue below

Recommended for you

RE: Fractionator feed furnace multiple passes

Ideally, there should be flow controller / control valve and FSLL on each pass. Second preference is balancing valve with flow indicator and FSLL on each pass, with balancing valve adjustment to be done during first startup. Do you have a PID for this furnace showing passes? What type of fractionator is this? - brief intro required.

RE: Fractionator feed furnace multiple passes

(OP)
Product stripper bottom feed to fractionator feed furnace in the Hydrocracker unit.

RE: Fractionator feed furnace multiple passes

Diagram is not clear, but I can see only 2 control valves which appear to be on flow control. What about the other 6 ?

In any case, either you adjust pass flow by FIC or by manual balancing valve. Keep flow at above low flow limit for each pass. Startup flow should be equivalent to min firing rate at this furnace. See ops manual for the furnace for min permissible flow and min firing rate for startup. Ramp up rate for firing should be within permissible ramp rate for product leaving the furnace; it may be 50degC per hour or similar.

RE: Fractionator feed furnace multiple passes

Presume the furnace pass flow controllers are FC 0811 to FC 0818. Check the ops manual for min permissible total flow to this furnace. Looks like there is some flow ratio control incorporated, so flow to each pass is automatically set to be the same.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close