I've read a handful of past threads on this, but wanted some assurance I'm doing this correctly.
To determine the design moment we take: Sd*Mstrength
This would then be compared to M=As*Fy*(d-a/2)
I'm checking a design that calculates Sd=fy/fs (assume phi and gamma are 1.0) and then take Sd*Mservice. The design then compares that amplified moment to M=As*Fy*(d-a/2).
I seem to be able to get a little more out of my section if I actually calculate Sd using phi=.9 and gamma equal to my load factor.
I'm a bit confused. What is S_d? There is a value, S, know as the environmental factor. Your moment demand is always multiplied by S=1.3. Shear is also multiplied by S=1.3 if additional shear capacity from steel, Vs, is required.
You need to determine the controlling load case, U, and multiply it by S. Which version of ACI 350 are you using? I don't recall seeing S_d.
This is ACI 350-06. To my knowledge this is the newest version of this code.
Sd is indeed the environmental durability factor. It is not always 1.3. The equation (9-8) is (phi*fy)/(gamma*fs).
How interesting. I was not aware of this change from '01 to '06. I wonder if my firm has continued with S=1.3 based off the commentary - see C.9.2.9.1.
Do you only have one load factor (i.e. soil/fluid load on a wall)?
Yes, ACI 350-06 and Sd is the latest code approach in the US. Rabbit12 did you read the commentary next to that equation?
ACI 350-06 Commentary R9.2.6 seems to suggest that the design approach you are asking about listed above may be valid depending on what your "M" value represents
A couple of questions:
1. Assume this is for a tension-controlled section?
2. You are holding Sd >= 1.0 for your checks, right?
3. Are you including phi for LRFD checks on your capacity side? You didn't explicity list if your "M" value included any resistance factors.
Something not right here. Assume Mservice is non-factored moment,
Mstrength = LF*Mservice
Mu = As*fy(d-a/2)
Mu = Sd*Mstrength = Sd*LF*Mservice = (fy/fs)*Mservice ??? The last expression is valid in this form," = Sd*(fy/fs)*Mservice", in which fy/fs = LF, and fs is steel stress calculated using ASD.
For last expression to be valid, fy/fs must equal to Sd*LF, however, you told us that in the calculation, Sd = fy/fs, where is the LF then? And what is fs, how was it determined? Quite confusing here.
In ACI 350-06 fs is a permissible tensile stress value that varies from 17 ksi - 24 ksi depending on whether there is one-way or two-way action and depending on the severity of the environmental exposure.
I'm confused by some of the nomenclature being used here: Rabbit12's vague "M" and retired13, I'd swap your Mu for phi*Mn, and your Mstrength for Mu. Where is your phi?
Usually we just divide phi*Mn by Sd and check against Mu. Use your typical phi and gamma values per the code to calc Sd. That may be a simpler approach :)
structbells,
I have read the commentary. It's pretty confusing to be honest.
To answer your questions:
1) Yes, let's assume tension controlled.
2) Yes, Sd must be greater than or equal to 1.0 per equation 9-8.
3) Which M are you referring too? The M=As*fy*(d-a/2)?
I really think this is just a general question more so than explicitly about "my" design. It seems to me if you want to use service level moments you need to take Mservice*Sd and compare that to M=As*fs*(d-a/2) if you want to use fy instead of fs you'd need to add the load factor to the Sd*Mservice calc.
I dropped strength reduction factor for simplification. The only thing I wanted to point out is that there is a missing term in the whole mix - the equations do not equate.
From earlier version of ACI350,
9.2.8 — Required strength U shall be multiplied by the following environmental durability factors (S) in portions of an environmental engineering concrete structure where durability, liquid-tightness, or similar serviceability are considerations.
So, ØMn = ØAs*fy*(d-a/2) >= Sd*Mstrength= Sd*LF*Mservice
Sd = 1.65 for axial tension, 1.3 for flexural, and 1,3 for excessive shear carried by shear reinforcement.
retired13, think I've got it. I'll use your LF designation instead of ACI 350's "gamma" for clarity:
If we substitute in Sd = Ø*fy/(LF*fs) into your expression on the right, we get:
ØAs*fy*(d-a/2)>= Ø*fy/(LF*fs)*LF*Mservice
Let the LFs and Øs drop out and you get:
As*fy*(d-a/2)>= fy/fs * Mservice
Does that clarify things Rabbit12 and explain the commentary section now?
Clever! Well explained. Thanks.
strucbells,
Thanks for that explanation. When I first looked at the calculation we were comparing a service load to a capacity calculated with Fy. That seemed like we were comparing apples to oranges, especially since we actually calculated Fs.