Masonry wall out of plumb
4

Masonry wall out of plumb

Masonry wall out of plumb

(OP)
I have a project that I am working on that is currently under construction (IBC 2015). The building is a single-story masonry bearing building supporting open-web steel joist and metal decking. Steel erection began last week and today I was told by the steel fabricator (who I work very closely with) that the masonry wall is out of plumb over 120’ of a 300’ long masonry wall. The wall is quite tall 29’ and I have been on the GC from the beginning about proper construction of the perimeter walls.

I don’t know exactly why the wall is out of plumb. I am guessing it wasn’t quite properly braced as during my last site visit, I found a large brace that wasn’t anchored to the deadman. It is in this area that the wall is out of plumb.

How do you go about fixing a masonry wall that is out of plumb? I can’t say that in 20 years I have ever had this happen before.

The out of plumbness is causing joist bearing issues on the wall (which is how this error was picked up).

I am not exactly thrilled at the moment.

RE: Masonry wall out of plumb

Since the deflection is affecting the proper bearing for the joist, it looks like some masonry re-work is required to correct the problem. The tricky part is to determine how much works to be removed and redone, and how much you want to shield the contractor for the burden he is obligate to bear. A good measurement should be the first step towards finding a good/reasonable solution.

RE: Masonry wall out of plumb

the last time i had an out-of-plumb wall... my speculation was that they were grouting too soon after it was being layed and they were only checking plumbness on the new work and not the post-grout work below.

RE: Masonry wall out of plumb

A 29' high by 300' long wall is a very large risk to leave exposed to the wind for a long time with only temporary bracing. The danger of blowing over is a factor to consider even when bracing is carefully installed.

If the out-of-plumb distance is not too large, the contractor may be able to ease the wall back to nearly plumb condition using cables and ground anchors each side of the wall. A 29' high wall should be fairly flexible, but it would be exacting work and should be followed up with joist attachment as soon as possible after or, better still, during the plumbing operation.

BA

RE: Masonry wall out of plumb

(OP)
Well, it's the next day and I'm still not thrilled (after a sleepless night).

I think we need to figure out what exactly is wrong in the field. Is the whole wall tilted, it the last course laid wrong, is there something else going on that we don't know about.

I am sure the GC is going to pursue easing the wall back (pushing the wall back). At that height I don't think it is going to take much force. I just want to know what options are on the design end before we have a conversation with the GC.

I was very skeptical at the beginning about building these walls. We have done another wall of this height with the GC in the past without incident so I knew it was possible and they were capable, but I still didn't like it.

RE: Masonry wall out of plumb

I am not so confident on the strength of the wall after straightening by force, will all the bond remain unaffected? Also, how thick is the wall?

RE: Masonry wall out of plumb

Wall thickness and reinforcing might help as well as a rough plan of the building showing interior column lines and shear walls or lines of permanent bracing, if any.

BA

RE: Masonry wall out of plumb

(OP)
Wall thickness is 12" (we just met the h/t requirement of 30 in ACI). The overall building is 600' long with an expansion joint about in the middle with a concentric steel brace along each side of the joint. No perimeter columns along this wall. The perimeter walls act as shear walls to resist lateral loads (since there was miles of masonry around the perimeter).

From talking to the client today it appears as if this is an isolated issue (withing 1-2 panels of masonry). I was told 9 joists do not have proper bearing (so that is 45' in-between those 9 joists). They are not exactly sure what went wrong yet as they are still trying to figure it out. The wall is way out of the 1/2" tolerance specified in ACI.

I suppose I could go back and check the wall for additional eccentricity. If I remember correctly, axial load was as much of a concern as bending (we specifically detailed joist bearing to fall within the h/t requirements of the code). I don't want to be the one to "fix" this form them. Their problem should not become my problem.

RE: Masonry wall out of plumb

I think how easy it is to flex back will depend on how much steel is in place. If little steel is installed, and you have bond beams, I would rent some meadow Burke braces and slowly rotate back. That is assuming the it is a simple case of some accumulated errors and not some real sloppy work.

If you really want to know how far out the wall is hire a 3D laser scanner company to scan the wall. We do this type of work with our 3D scanner, and it is easy when it is a clear open space. It could be as little as one scan where it will take longer to setup than do the actual scan. Our scanner will collect data from as far as 1100ft in the right conditions. When done, they can give you a file that shows you the true wall shape within mm's. I will post a couple of screenshots shortly of a floor slab and wall structure we did not long ago.

RE: Masonry wall out of plumb

I'm surprised they even braced the wall, in my area I see CMU walls that tall being built all the time without any bracing. With what ever decision you make, keep in mind that you accept a great deal of liability if you let them rotate the wall back rather than rebuild it.

RE: Masonry wall out of plumb

(OP)
Steel is installed but not physically attached to the wall yet. They realized they have and issue so the roof members have not been attached to the wall. They have a style of Burke braces installed in the field as temporary shoring already. We did place bond beams at window head, mid height and under the joist bearing (which works out to the 1/3 points of the wall).

Out of curiosity, I went back into my computer models and modeled the eccentricity of the new wall on the applied dead and snow loads (using the eccentricity on the full dead which isn't quite right as the weight of the wall is a large portion of the dead load). After a 5 minute heart attack (forgetting how the NCMA software works for 5 minutes) it appears as if the wall has sufficient reinforcing to resist the as-built eccentricity.

I don't know what I am going to do. I want to see if the GC will come up with a pleasing solution (doubtful). I am sure this will not be resolved until sometime next week. Until then I will ponder the options.

RE: Masonry wall out of plumb

Here is an example scan as mentioned. Keep in mind this is not a picture. The scanner creates colored points and collects enough points that the data looks like a photo when done.


From the data you can create a contour map like the one below.


This was one of the worst slab on grades we have scanned. It has heaved over 9". Here we could use a contour interval of 1"'s and not 1/8 ths like typical.

RE: Masonry wall out of plumb

Brad - that's pretty neat. What kind of scanner is your company using, and what kind of file output does it deliver? What about post processing requirements?

RE: Masonry wall out of plumb

We are using a TopCon GLS2000, but would like to upgrade to the new Leica RTC360. Leica and Faro are the more common scanners. Registering scans together can take some time if you have lots of scans, but the new RTC does a pre-registration as you are scanning since it tracks the scanners position. We hope that will speed up the process of registering the data. The scanner is essentially collecting million of points, and 360deg photographs. The points are colored automatically based on the photographs. At the end of this you have a point cloud that can be read with Autodesk Recap, imported into Revit, CAD, or many other packages that can handle very large point files. The top image was taken from the Revit model. Converting the data into a solid model after this can be tricky. There are endless software solutions for different aspects, and you may require many software packages when involved in multiple industries. In a case like this one could easily figure out the wall deformation by measuring in Recap to find the wall bow.

There are some other nice scanner solutions on the market too that are much more cost effective. The progress being made in photogrammetry is quite impressive and it is quite a bit easier to work with. The Leica BLK360 can collect data that can be accurate to within 1%. This would not work well for this case if dealing with long distances, but if you are wanting to create decent general arrangement drawings for a reno, it can be a great option.

RE: Masonry wall out of plumb

What about welding extensions on the bar joist seats? I guess cutting the metal deck and massaging the edge angle to conform to the bow could be a bummer.

RE: Masonry wall out of plumb

Quote (Aesur)

29 May 20 18:31
I'm surprised they even braced the wall, in my area I see CMU walls that tall being built all the time without any bracing. With what ever decision you make, keep in mind that you accept a great deal of liability if you let them rotate the wall back rather than rebuild it.

Would the masonry contractor's insurance policy cover an unbraced wall if it blew over in a 30mph wind?

BA

RE: Masonry wall out of plumb

BART... I don't think I've ever seen a masonry wall built that high... on a positive note, if it can be restrained by the roof diaphragm, it takes little force on 29' to hold it in place... might not be that difficult a problem...

Dik

RE: Masonry wall out of plumb

dik,

The concern is temporary braces during construction of a 3 story high masonry wall. At this stage, it is a cantilever, the slenderness ratio of this wall approaches 200, quite flexible and vulnerable.

RE: Masonry wall out of plumb

retired13... no doubt about it... bracing is essential... but, correcting the out of plumbness may not be as big an issue...

Dik

RE: Masonry wall out of plumb

I image the mortar-brick bond is likely to be damaged to an extent, wouldn't it be a concern, and how to correct it, maybe re-patch?

RE: Masonry wall out of plumb

@BAretired, I cannot say if their insurance policy would cover it or not as I am not privy to sub contractors or contractors insurance policies and I'm sure they vary significantly in coverage in the industry. I can however see that if the EOR allows the wall to stay as is or gives any inclination of it being ok then his insurance could find themselves dealing with it should it fall. There needs to be a fine line between means and methods and in this case it is my opinion the contractor should pay the EOR to find a fix, even if if it is tear down and replace, but the EOR needs to be careful in how they proceed with recommendations and should consider telling them they need to hire a shoring engineer to determine if shoring is needed.

I have unfortunately seen a CMU wall fall because it wasn't shored/braced before the finished structure was in place, relying on the finished structure (diaphragm) to brace it once everything is built. The contractor didn't brace it, the wall came down, the EOR helped them in finding a solution to reuse some members that were twisted and in doing so opened himself up to a claim against his insurance because the contractor used the new connections, that held the twisted members in place after bending back to the right position, against the EOR claiming the design was bad in the first place. Once a claim starts it get's expensive for the EOR just to fight it typically, usually costing more than the fee for the project even was. Because of seeing this and other claims against engineers in the past I tend to be cautious in how to respond to contractors who are typically out to save money, cut corners and figure out ways to have change orders or make someone else pay for their mistakes. There is something seriously wrong with this industry where the contractors make huge profits and the engineers make little profit yet have to do most of the thinking for the contractors.

RE: Masonry wall out of plumb

I've little reservation on Aesur's responses on whether building a 29' masonry wall is a typical/common practice or "atypical". If it is occurs quite often, then the typical contractors would have enough knowledge and experience, and be the sole responsible party for the success or fail. However, if it is atypical (not so common), then the construction procedure (care) and qualification of the builder should often be addressed during the bidding process. The engineer could be held partially responsible if the risks are not properly/clearly communicated in the design document.

When bad thing happens, the engineer shall act only through request of the owner, and/or request for corrective action by the contractor, all on papers and be documented. The engineer shall only issue corrective measures, that has no doubt in mind, to restore the failed structure back to the original design without adding extras. Everybody still can elect to sue anybody, but your base is covered through proper documentation of the development.

RE: Masonry wall out of plumb

Aesur,

I was a little taken aback when you expressed surprise that a 29' high by 300' long masonry wall was braced and that in your area, similar walls are routinely unbraced. NCMA have recommended requirements for bracing masonry walls during construction. If the contractor cannot show that NCMA requirements were met or exceeded, he runs the risk of having his insurance claim rejected in the event of collapse due to wind.

I can't say that I agree that the contractor should retain the EOR to find a fix, as that would be a potential conflict of interest. The EOR is likely to find himself in a can of worms if he instructs the contractor on measures to be taken to fix the wall or even if he provides advice on how to fix it. Your recollection of a similar incident where the EOR opted to help the contractor is a case in point.

BA

RE: Masonry wall out of plumb

I am not doubting that it happens, but not bracing a wall that high is grossly negligent. Similar to unbraced trenches in that regard, and both cost lives.

RE: Masonry wall out of plumb

@Retired13 & BAretired, I wanted to clarify that I see walls built that tall all the time in my area of the country without bracing, not that I agree with it. In my earlier post I was saying I was surprised because in my area it's not common to brace it; not that I'm surprised because it isn't needed. I believe masonry walls should be braced when being built. Sorry if my sarcasm caused a little confusion.

Based upon the research I have done, per OSHA if the wall is over 8' (if I recall correctly) off the ground it must be braced. However bracing can be done with 2 methods, one with physical braces, the other by creating zones that cannot be entered and continuously monitoring the wind speed and evacuating the site when the wind gets too high, at least that was my understanding from a quick read.

@BAretired, you make a great point about not hiring the EOR for the fix; however I see all too often that the EOR gets brought in when the contractor messes up and is expected to fix it by the owner and architect, usually for free. It's a tough spot to be in from a client relations standpoint. It is definitely best to get a contract in place before even talking about how to fix it and to get it in writing what happened, why it happened, and who was at fault to try to avoid costly lawsuits.

RE: Masonry wall out of plumb

2
If you really want to know more about bracing masonry walls you need to get a copy of "Standard Practice for Bracing Masonry Walls Under Construction" (Dec. 2012) published by the Mason Contractors Assoc of America (www.masoncontractors.org) but developed by the masonry industry. It provides the maximum height of unbraced walls, evacuation requirements during certain wind speeds and connection design. It takes all the guess work out of bracing masonry walls during construction. NCMA's technical literature follows the same guidelines. Tbere are also publications about the use of internal bracing where the reinforcing steel is used to temporarily support the wall while the strength increases (http://imiweb.org/wp-content/uploads/2015/11/IMIIn... and https://www.structuremag.org/?p=2016). This is a life safety issue and should be taken seriously. While this is beyond the OP's question, I thought it was important to bring up.

RE: Masonry wall out of plumb

When bad thing occurs during the life of the constructed structure, the engineer is rarely not affected, and is very unusual not to get involved. Depending the nature of the issue, any advice, opinion, corrective action should be issued/offered with "no cost to the owner" and "holding no harm to.." clauses clearly stated. To me, stay silent is not a good way to avoid liability, which could be assigned by the accuser, or his attorney anyway. Showing care and proper concern usually go a long way.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - Strategies to Secure Connected Cars with Firewalls
White-hat hackers have demonstrated gaining remote access to dashboard functions and transmissions of connected vehicles. That makes a firewall a vital component of a multilayered approach to vehicle security as well as overall vehicle safety and reliability. Learn strategies to secure with firewalls. Download Now
White Paper - Model Based Engineering for Wire Harness Manufacturing
As complexity rises, current harness manufacturing methods are struggling to keep pace due to manual data exchanges and the inability to capture tribal knowledge. A model-based wire harness manufacturing engineering flow automates data exchange and captures tribal knowledge through design rules to help harness manufacturers improve harness quality and boost efficiency. Download Now
White Paper - What is Generative Design and Why Do You Need It?
Engineers are being asked to produce more sophisticated designs under a perfect storm of complexity, cost, and change management pressures. Generative design empowers automotive design teams to navigate this storm by employing automation, data re-use and synchronization, and framing design in the context of a full vehicle platform. Download Now
eBook - Simulation-Driven Design with SOLIDWORKS
Simulation-driven design can reduce the time and cost of product development. In this engineering.com eBook, we’ll explore how SOLIDWORKS users can access simulation-driven design through the SOLIDWORKS Simulation suite of analysis tools. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close