steel canopy - anchoring into the existing structure
I'm designing pretty big steel canopy next to the existing residental buidling.
I am planning to anchor steel beam (blue in image) to existinc concrete wall.
Since vertical reactions at the end of the beam is quite large = 45 kN I'd like to anchor it as shown in attached sketch. That way I get shear forces only (on the bolts) right? So I have to control welds (beam - plate), bolts (shear) and steel plate (to shear).
Thoughts?
Any other/better solution will be appreciated
RE: steel canopy - anchoring into the existing structure
You’ll get some tension in the anchor bolts too because the connection is semi rigid.
what if I use only one row of bolts instead of 2?
You get horizontal force and tension force due to the bracing too ...
Yes, I do but they are not that large.
You should have no problem with that load into the wall. (4) 3/4" Hilti anchors should be able to handle the 45 kN and achieve some tension capacity as well if you need it. If you want to weld the tube to the plate you can just weld each long side to the plate and leave the tops un-welded. You should be able to develop 45 kN over the length of those welds. I would also spread the anchors out vertically as much as you can to reduce their interaction with one another.
If you have other shear/tension forces from the braces I would include those unless they are legitimately negligible.
Check out the anchor capacity with the Hilti profis software. As long as you have no edge distance issues in the concrete I believe you can handle those loads no problem.
I agree with Tomfh,
The beams will rotate under load, and this will cause tension in the bolts whether you have 4 bolts or 2.
That tension should be included in the design of the bolts along with their shear forces.
Another idea would be to bolt on a plate to the wall, then weld on a perpendicular single plate shear connection with horizontal slotted holes - allowing some rotation and negating rotational bolt tension.
That detail, though, doesn't allow for any axial tension in the beams to pull on the connection, or wall; so any tension on your overall framing from wind would have to be taken some other way - or you simply include it as direct tension in your bolts.
Use a larger, thinner plate for your connection that will flex before it puts too much prying action into the bolts.
Yes a more flexible plate that cannot develop significant tension in the anchors is a neat way to do it.
So I presume that there will be some kind of load on top of this structure?
Larger plates would be a very good idea.
P.E. Metallurgy
1) The flip side of using a flexible plate to limit connection moment demand is to use a stiff member. Things look a lot different at L/480 than they do at L/90.
2) For me, the difficulty with thin plate path is estimating how flexible the damn thing actually is. By the time that you're suitably conservative on plate bending and prying behavior, you often wind up back at "pretty stiff". And the thinner the plate, the more the prying action factors in.
3) On occasion, I've used a single row of bolts and small plate washers behind the connection plate to try to encourage pin-ish behavior. I'd not want to do that on a connection like this with aesthetic implications however.
Don't you have lateral load? The rebound of wind from the building wall can push the canopy outward and create instability, not to mention earthquake effect.
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
Research Report - How Engineers are Using Remote Access
Remote access enables engineers to work from anywhere provided they have an internet connection. We surveyed our audience of engineers, designers and product managers to learn how they use remote access within their organizations. We wanted to know which industries have adopted remote access, which software they are using, and what features matter most. Download Now
eBook - Managing the Context of Product Complexity Using the Digital Twin
Keeping track of changes to complex products is difficult—think Aerospace & Defense equipment, new generations of commercial aircraft, and software-based automobiles. A new way to managing the digital context of the physical product is required and the answer is the Digital Twin. This ebook explores the opportunity available for Operations and Maintenance for the Digital Twin. Download Now
White Paper - Trends in Industrial Filtration
Substantial progress has been made in filtration technologies in recent years. New filter media materials, designs and processes have led to filters that are more efficient, reliable, compact and longer lasting. This white paper will discuss the various trends that are impacting operational responsibilities of MROs today and the resources that are available for staying up-to-date on the latest filtration solutions. Download Now
Close Box
Join Eng-Tips® Today!
Join Us             Close