Design load for column/joint retrofitting in case of Strong Beam-Weak Column behavior

Design load for column/joint retrofitting in case of Strong Beam-Weak Column behavior

Design load for column/joint retrofitting in case of Strong Beam-Weak Column behavior

(OP)
BACKGROUND INFO
I am checking the design of an existing G+1 building with a total plan dimension of 25m (L), 9m (W) and a height of 14.8m, as shown in following fig.


There is a standard live load of 100 psf on first floor and, equipment loads (provided by supplier) at roof level. The height of this equipment is almost 13 m and is similar to as shown in the following fig.


The structure of the building is supposed to be IMF moment frame subjected to Zone 2B earthquake loads. The design check of the structure shows that beam column capacities are adequate but structure shows a “strong beam and weak column” behavior. Thus, columns and joints are proposed to be retrofitted using FRP by specialized consultants. I am responsible to provide them the required column and joint capacities for FRP design.

QUESTON

I am using the following methodology to achieve this goal. I’ll be thankful if someone could confirm if what I am doing is right or if I am way off my rockers.

I am using sap2000 to perform a push over analysis and a sort of performance-based design. I am not going too deep into performance-based design because my understanding is very limited. My goal is to find the load at which beams will go into plastic region before the columns.

For push over analysis, I first loaded the structure with D + 0.5L + 1Equip. and then incrementally pushed the frame upto 0.02h. I’ve assigned auto generated plastic hinges as per FEMA-356 to frame members, “M3 hinge” at beam ends and “P-M2-M3 hinge” at column ends. Although I’ve a good theoretical understanding how a M3 hinge behaves. I cannot say the same about P-M2-M3 hinges. I’ll be obliged if someone could provide me with a good reference on the subject matter or can explain the behavior in detail.

Also to provide some of the facts, while modelling this nonlinear behavior,
1. I’ve not taken into consideration the extra rotation due to (i) Cracking at negative moment region and (ii) Shear cracks. At this level, I consider this a conservative assumption for column and its joints, because the more load a beam can take, the higher the design load will be obtained for column design from analysis. I am aware that this might not be the most economical option for client.
2. I’ve considered the true stress-strain curve of the rebar and not the conventional perfectly plastic model because I believe the rebar will be in strain hardening regime at higher EQ loads.
3. I’ve also considered cracked property modifiers for frame sections (0.5 for beams and 0.7 for columns).

I’ll report the forces in column for FRP design at that “step” in which rotation in beams reached the “Life safety” range as per FEMA. These forces will not be increased using a load factor. I’ll be thankful if someone could confirm if what I am doing is right or could suggest a better way to find the design load.

RE: Design load for column/joint retrofitting in case of Strong Beam-Weak Column behavior

Seeing as nobody else has taken a swing at this, you may have to settle for my input. At the least, you'll get a thread bump out of this.

1) If it is at all possible, I would forgo the entire pushover analysis and simply reinforce the columns and joints to make them stronger than the expected beam hinges tying in with overstrenth etc. This wold be much simpler analytically, I feel, since you'd just work out the capacities of the beams and use those for the loads on your columns and joints.

2) I agree that performance based design is a viable strategy here but, if that's your path, then I think that you have to take it all the way rather than in half measures. I think that what you'd want to do with PBD is to convincingly demonstrate that your beams won't need to develop plastic hinges. Once you've concluded that plastic hinges are required, no matter your analysis method, I think that you are obligated to satisfy the strong column / weak beam requirements.

3) Note that your roof level beams do not need to satisfy the strong column / weak beam requirements. That will only be necessary at the second floor framing where those requirements will be much easier to satisfy.


RE: Design load for column/joint retrofitting in case of Strong Beam-Weak Column behavior

What is the motivation for the retrofit, and where is the intended FRP application? For industry equipment, stability is often out weight flexibility, is plastic hinge a desirable feature in such a low seismic zone?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Research Report - How Engineers are Using Remote Access
Remote access enables engineers to work from anywhere provided they have an internet connection. We surveyed our audience of engineers, designers and product managers to learn how they use remote access within their organizations. We wanted to know which industries have adopted remote access, which software they are using, and what features matter most. Download Now
eBook - Managing the Context of Product Complexity Using the Digital Twin
Keeping track of changes to complex products is difficult—think Aerospace & Defense equipment, new generations of commercial aircraft, and software-based automobiles. A new way to managing the digital context of the physical product is required and the answer is the Digital Twin. This ebook explores the opportunity available for Operations and Maintenance for the Digital Twin. Download Now
White Paper - Trends in Industrial Filtration
Substantial progress has been made in filtration technologies in recent years. New filter media materials, designs and processes have led to filters that are more efficient, reliable, compact and longer lasting. This white paper will discuss the various trends that are impacting operational responsibilities of MROs today and the resources that are available for staying up-to-date on the latest filtration solutions. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close