Looped fluid system
Looped fluid system
I have a system which heats a fluid while in a constant flow in a loop
how would i calculate the energy used to heat the fluid in the looped system to the temperature set and the time to reach it
sorry if i put it in the wrong forum
thank you
thank you
RE: Looped fluid system
Does this loop exist?
If you're trying to come up with a heater size for this existing loop you can use the pump power against the temperature rise of the media circulating in the loop to estimate the power needed to get to a higher temperature.
Keith Cress
Find the heat capacity of the fluid, the mass of the fluid and how fast you want the temperature to rise.
Allow a certain maount for heat loss of the loop, unless its very well insulated.
for a closed loop you can probably forget the power put into the system by the pump.
Keith Cress
Thank you for more properly spelling out your requirements.
CR
Im using heat transfer oil so as i raise in temperature more the specific heat capacity also goes up
for example from the data sheet at 100 degrees Celsius:
the density of the oil is 811 kg/m 3
the specific heat capacity is 2.173 kJ/kg*K
and the thermal conductivity is 0.128 W/m*K
from testing the heating unit say that it flow at 49 L/min at 100 degrees Celsius
and also at 300 degrees Celsius
the density of the oil is 681 kg/m 3
the specific heat capacity is 2.902 kJ/kg*K
and the thermal conductivity is 0.114 W/m*K
Also from testing the heating unit say that it flow at 43.9 L/min at 300 degrees Celsius
if this helps more ?
Energy or heater power??
You need total mass for both.
You need time from one temperature to another for power
~you can probably average the heat capacity between your two end points.
This will only be an approximate figure as you don't say what sort of heat losses are happening
how much energy is used to heat the oil
how long the oil can hold heat for
how long it'll take theoretically for the oil to heat up to temperature
and how long it'll take the oil to heat up 2 tools made of mild steel weighing around 90kg each
the loop contains 18L of oil if this is what is meant by mass ??
and the heating unit is 24kw and running around 2.5 bar
Thanks for the help
18litres is a vlume, but you know the density so you can work out mass ?(kg)
That's a pretty big heater for only 18 litres of oil. I suspect the surface temperature of your heater might be an issue and you could "cook" the oil unless you're flowing really fast through the heater elements.
Either that or the heater elements will burn out because they will get too hot.
Heat up time I get is about 5 minutes from 100C to 300C. In theory.
the oil is flowing through fast so the oil isnt being cooked and elements wont burn
please can you comment the equations that need to be used as that would be a big help thanks as i dont understand where i can find them or if they are even the correct ones
Heat Transfer: Introduction to Heat Transfer (1 of 26) by CPPMechEngTutorials
https://www.youtube.com/watch?v=TWTQx3W-2k8