Beam sitting on end of wall

Beam sitting on end of wall

Beam sitting on end of wall

(OP)
Hi,

I have a window lintol sitting onto a 100mm wall 90 degrees to the wall. But....It's at the end of the wall though. I'm not comfortable with the detail as the load spread is only in 1 direction. Anyone do this before??

Thanks.

RE: Beam sitting on end of wall

Haven't done it before, but I suspect you'll only get meaningful answers if you provide more information, including:

1) What (material) type of wall is it?

2) What is the height of the wall?

3) What are the vertical load from the beam and any lateral loading out of plane to wall (axial along beam)?

4) What is the width of the beam?

Whether it will work or not depends largely on how much of the wall is needed to support the beam load and whether the local region of the wall is able to distribute the load to that required length.

Rod Smith, P.E., The artist formerly known as HotRod10

RE: Beam sitting on end of wall

Quote:

I have a window lintol sitting onto a 100mm wall 90 degrees to the wall. But....It's at the end of the wall though. I'm not comfortable with the detail as the load spread is only in 1 direction.

Need more descriptions on phrases in bold. A sketch will help.

RE: Beam sitting on end of wall

1) I assume that this is just a beam tying into a wall with the beam and wall oriented orthogonally.

2) I have done this.

3) As to whether or not it's okay, let the numbers be your guide.



RE: Beam sitting on end of wall

4" wall? Very light built, even for reinforced concrete.

RE: Beam sitting on end of wall

I’ve done this plenty of times. HOWEVER - if your lintel is the prestressed type acting compositely with the masonry above (reliant on arching above) then no, you don’t have enough beef in the orthogonal support wall to resist the horizontal thrust.

RE: Beam sitting on end of wall

(OP)
Hi Mistructe_ire,

Having thought a bit more about it I'm going to reduce the window width and creat a 200mm end bearing for the lintol. I'm going to use a heavy duty lintol which is effectively a UB.

Cheers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close