In the past, ACI 318 (Appendix D) has largely dismissed the idea of supplemental reinforcement for pryout failure. Does ACI 318-14 discuss this subject? Is there any research as of yet to address it?
What I have is a anchor that is 1.5" in diameter, embedded 12". Most research precludes pryout failure at this embedment. (I.e. 5d or greater.) But what worries me is: there is a edge 6" away from the bolt. It is not loaded towards this edge. (The edge in the direction it is loaded is 30" away......even further in other directions.) To be sure there is a hairpin arrangement that could take this out. Thanks.
What I have is a anchor that is 1.5" in diameter, embedded 12". Most research precludes pryout failure at this embedment. (I.e. 5d or greater.) But what worries me is: there is a edge 6" away from the bolt. It is not loaded towards this edge. (The edge in the direction it is loaded is 30" away......even further in other directions.) To be sure there is a hairpin arrangement that could take this out. Thanks.
RE: Pryout Reinforcement
I don't think the code explicitly covers this, but pryout is inherently a tension cone failure, so it makes sense to design the supplemental reinforcement on that basis. But I think horizontal hairpins at the anchor head could also prevent pryout, since the anchor head becomes restrained from rotating and popping the concrete up behind it. It's kind of a judgment call.
RE: Pryout Reinforcement
RE: Pryout Reinforcement
a) For supplementary reinforcement, it's set up in such a way that it's pretty clear that they don't intend for that to be used for pry out.
b) For true anchorage reinforcement, the only make specific reference to shear breakout and tension breakout.
2) A PCI paper on pryout indicates that it's not an issue for hef/d < 4.5 which is consistent with what you mentioned. That said, they don't really say anything about the case of rear anchors near a free edge.
3) The rear anchor cracks shown below are suggestive of your rear edge distance concern.
4) I really do think that the character of this changes substantially with long-ish anchors. I'll noodle some on a) finding a way to justify no prying action and b) the best way to reinforce for prying action given expected behavior.
RE: Pryout Reinforcement
The thing I have to wonder is: if I have good bearing on the side of the bolt (with a pretty conservative model).....and 8d embedment......can it really pry out (even with that close edge on the back end)? Will read on this some more myself.
RE: Pryout Reinforcement
RE: Pryout Reinforcement
It's tempting to think that but, then, look at the pictures above. Clearly, at some degree of separation, you produce separate, and apparently different, pryout phenomena.
RE: Pryout Reinforcement
No doubt. Fundamentally, the source of pryout is the eccentricity between where the shear is delivered (plate) and where it is resisted (a little below the plate). So the general tendency is there with any proportion of anchor. With the short and stocky, we seem to understand the mechanism. The anchor does kind of a rigid body rotation along with the up and out diagonal kickback thing. With a long anchor, I'm not sure that I know the mechanism. I sketched up a few things but didn't have any real confidence in any of them. Regardless, with a longer, skinnier anchor, I'm confident that your prying action exhibits the following features:
1) A greater lever arm for the concrete compression stresses that ultimately resist the applied eccentricity. Ergo much smaller resisting couple loads.
2) Pry out demand that tends more to wards kicking out than kicking up and out.
Both of the those things help but, of course, the questions is how much. #2 leads me to believe that hairpins parallel to load are the way to go for this. But then I'm unsure where to place them best perpendicular to the load. maybe just add a pair at 3" oc near the bottom of the anchor and call it a day.
RE: Pryout Reinforcement
RE: Pryout Reinforcement