WARose
Structural
- Mar 17, 2011
- 5,594
In the past, ACI 318 (Appendix D) has largely dismissed the idea of supplemental reinforcement for pryout failure. Does ACI 318-14 discuss this subject? Is there any research as of yet to address it?
What I have is a anchor that is 1.5" in diameter, embedded 12". Most research precludes pryout failure at this embedment. (I.e. 5d or greater.) But what worries me is: there is a edge 6" away from the bolt. It is not loaded towards this edge. (The edge in the direction it is loaded is 30" away......even further in other directions.) To be sure there is a hairpin arrangement that could take this out. Thanks.
What I have is a anchor that is 1.5" in diameter, embedded 12". Most research precludes pryout failure at this embedment. (I.e. 5d or greater.) But what worries me is: there is a edge 6" away from the bolt. It is not loaded towards this edge. (The edge in the direction it is loaded is 30" away......even further in other directions.) To be sure there is a hairpin arrangement that could take this out. Thanks.