Due to the wide variation of requirement, we suggest getting a qualified Power Engineer familiar with the local engineering practice to develop a preliminary design and major equipment specs.
Usually, local power utilities is a good source that might help with typical design and specs for different applications including owner substation that will help to determine the usual equipment to be connected to the utility power network.
A generic partial list is suggested as follow:
* Protective device: Fuses, circuit switcher, circuit breaker (live or dead tank)
* Disconnect Switch: Vertical break, double break, center break, etc.
* Instrument transformers: PT or CCVT & CT (not required for fuses, free standing CT for live tank or bushing CT for dead tank Bkrs.)
* Transformer & Reactors: Power Transformer (with or without tap changer), distribution trasformer for auxiliary station power, regulating transformer (if NLTC) is provided in the main power transformer.
* Shunt Capacitor bank for voltage regulations.
* Protection and control: Relay and control panels (not required for fuse), revenue meters.
* Surge Arresters: (transformer usually furnished with arrester)
* AC & DC Aux. Power Subsystems: LV protective devices (MCCB and/or fuses), panelboards, transfer switches, batteries, battery chargers.
* Communication System: SCADA, power line carrier, telephone lines, etc
* Ancillary System: Lighting, security alarm, fence & gates, surveilance equipment (NERC CIP requirement, grounding (earthing), etc.
* Miscellaneous: Steel Support Structures, raceways (trenches, conduit, direct buried, etc.) fire wall and oil contaitment for transformers & reactors, HVAC for control house, fire suppression, drainage system, access road, etc.