Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power
8

Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)

Motor Data:
7.5 kW 230/460V 50 Hz.(Delta or Y Configuration)

Does the above mean if Plant supply 460VAC (more than likely 480VAC) is connected to the motor using a DELTA connection that it is running at 230VAC and if connected in a "Y" configuration motor is being supplied 400VAC?

Can this motor be used with incoming power (Plant power) set at 400VAC at 60 HZ using a VFD?

Thanks.



RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Are you sure you have that right?

400V 60Hz is only used in a couple of small countries, like Montserrat, Trinidad and Tobago (although it was used here in the US back in the 70s for IBM mainframes back when those were a thing). 460V 50hz is not used anywhere that I'm aware of. If your motor says that, it would not be a Delta/Wye connection for 230/460V because the voltage difference for D/Y is 1.732:1, not 2:1. You have miscommunicated something or are being given incorrect information somewhere.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)
Jraef,

You are correct. My mistake. It was 7.5 kW / 230/400VAC (and not 460VAC) / Delta/Y at 50Hz.

If I were to interpret the above...this tells me that I can supply the motor with either 3-Phase 230VAC or 400VAC at 50 Hz. Is that correct?

Which wiring configuration (Delta or Y) to use? What dictates which configuration to use?

If line voltage is 3 Phase 400VAC at 60Hz (not 50Hz), Can I wire up a VFD to 400VAC input but run the motor at 230VAC at 50Hz Max? (i.e. limit VFD Power output and Freq Output to the motor?)

Thanks.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Regardless of frequency, a dual voltage motor is connected in delta for lower voltage and in Wye for higher voltage.

Muthu
www.edison.co.in

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)
edison123,

Thanks, that clarifies the delta/Y connections.

Still looking for answer to the following.

230/460VAC at 50Hz (Motor rating)

What would the equivalent low voltage (for a DELTA Connection) be at 400VAC 60Hz line voltage?

Is it 200VAC. How do I figure that? ideally, I want the motor to behave exactly like it would at 230VAC (with a line input of 480VAC)in DELTA configuration at 50HZ, but with 400VAC and 60Hz using a VFD.

Thanks.





RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Again regardless of frequency, a 400 V wye connection becomes a 230 V delta connection.

Muthu
www.edison.co.in

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)
Edison123,

Pardon my ignorance. In the earlier post you said Delta is used for lower voltage and later you commented that "WYE" is used for lower voltage, both regardless of frequency. I get the frequency part.

In essence, you are also saying that 460VAC's lower voltage is 230VAC and 400VAC's lower voltage is ALSO 230VAC?. Unless I misunderstood what you were trying to convey.

There is so much conflicting information. I am trying to find the correct answer. Perhaps I might not be asking the question properly.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Please go back and read the name plate again.
230/460 is a common 60 Hz, 9 lead series-parallel connection. Ratio 1:2
230/400 is a common 50 Hz, 6 lead wye-delta connection. Ratio 1:1.73

230/460 50 Hz does not compute.
230/460 wye-delta does not compute.
Now if this is actually a 400 Volt, 50 Hz wye connected motor it may be operated on 400V x (60Hz/50Hz) = 480 Volts, 60 Hz.
The motor will run 20% faster but will have the same torque as at 400 V, 50 Hz.
You may configure the VFD for a motor of 480 Volts at 60 Hz, or for a motor of 400 Volts at 50 Hz.
Then dial the speed that you need.
But first, please, reread the nameplate.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Edison123 didn't post conflicting information.

For wye vs delta connections, the voltage ratio is always wye = 1.73 x delta.
For wye vs delta connections, delta is always the lower voltage and wye is always the higher voltage.

You can always set a VFD to produce an output voltage up to the line voltage being supplied. 400VAC supplied means the VFD can produce up to 400VAC on the output. 480VAC supplied means the VFD can produce up to 480VAC on the output. This is regardless of frequency. I've setup a VFD connected to 480VAC to produce 460VAC at 6.7Hz before.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

I apologize Columbo7. I missed your correction to 230/400 Volts.
However in my defense I note that after the correction you again posted the wrong (460V) voltage value.
Remember, as the voltage drops by a ratio of 1.73:1 the current increases by a ratio of 1:1.73.
Further to Lionel's post, you could set the motor up as delta at 230 Volts but the VFD will be more expensive than if you use a wye connection at 400 Volts.
At 400 Volts and 50 Hertz, the Volts per Hertz ratio is 8:1 This is important and should be maintained.
A 400 Volt, 50 Hz motor may be used on 60 Hz at any voltage up to 60Hz x 8V/Hz = 480 Volts, subject to load constraints.
If the V/Hz ratio is too high, the motor may go into saturation and quickly overheat.
If the V/Hz ratio is too low, the maximum safe torque will be less than optimum.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)
edison123,

My apologies about conflicting information. I misread your second post. You were correct in both.

Waross,

Unfortunately I do not have the nameplate or picture of it at the moment and won't be getting it from the customer for another month or so. You said...."Now if this is actually a 400 Volt, 50 Hz wye connected motor it may be operated on 400V x (60Hz/50Hz) = 480 Volts, 60 Hz."

It is. From the information that was given to me, it states;

7.5Kw
230/400VAC
D/Y
50Hz
Freq. Converter operation (S9) in DELTA connection up to 100Hz
7.5kW: 230VAC 3000 RPM at 50Hz
15kW: 460VAC 6000 RPM at 100Hz (How is this possible? In Delta configuration, shouldn't this be 230VAC? Or is it saying it can be supplied with 460VAC but motor will only see 230VAC?)

Going back to your statement;

"Now if this is actually a 400 Volt, 50 Hz wye connected motor it may be operated on 400V x (60Hz/50Hz) = 480 Volts, 60 Hz."

Does this mean I can operate this motor with a line voltage of 400VAC 60Hz (at VFD Input), but the motor will be connected in a Delta configuration where it will only see 230VAC at it's connections?

Thanks again for everyone's help.



RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

3
Motors follow really nice ratios when you use a VFD.

The motor always wants a constant V/Hz ratio to maintain a constant rated torque, so get the V/Hz first.
230/50 = 4.6 V/Hz

Now,
At 25 Hz, you'd want to apply 25 Hz x 4.6 V/Hz = 115 V
At 75 Hz, you'd want to apply 75 Hz x 4.6 V/Hz = 345 V
At 100 Hz, you'd want to apply 100 Hz x 4.6 V/Hz = 460 V

Since the rated torque remains the same, ratio the frequencies to get the rpm and HP at the different frequencies, so get those ratios.
3000/50 = 60 rpm/Hz
and
7.5/50 = 0.15 HP/Hz

This means:
At 25 Hz,
rpm = 25 Hz x 60 rpm/Hz = 1500 rpm
HP = 25Hz x 0.15 HP/Hz = 3.75 HP

At 75 Hz,
rpm = 75 Hz x 60 rpm/Hz = 4500 rpm
HP = 75Hz x 0.15 HP/Hz = 11.25 HP

At 100 Hz,
rpm = 100 Hz x 60 rpm/Hz = 6000 rpm
HP = 100Hz x 0.15 HP/Hz = 15 HP

Keep in mind that the above rpm's are the synchronous speed of the motor. It will always slip a bit. It may run at 50 rpm below the synchronous speed when at full load.

The short form reason why this works - To get a constant torque requires a constant magnetic flux. The flux is produced by current. Since the inductance of the coils varies directly with frequency you need more voltage to keep the current constant as you increase frequency.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)
LionelHutz,

Thank you so much for that detailed explanation. I am still a bit confused about the Delta & Wye configuration as it applies to incoming line voltage. Taking the following motor spec in to consideration;

230/400VAC
D/Y
50Hz

Does this mean I need 230VAC line power if I want to run this motor using the DELTA connection and 400VAC incoming line power to connect it using the Wye configuration? I was under the assumption if I had incoming power at 400VAC I can still use that to run the above motor configured in a DELTA configuration and the motor would see 230VAC as its supply voltage.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

"I was under the assumption if I had incoming power at 400VAC I can still use that to run the above motor configured in a DELTA configuration and the motor would see 230VAC as its supply voltage."

You are wrong. As the nameplate and others have clearly stated here, if your source is 400 V, you connect the winding leads in wye and if your source is 230 V, you connect the leads in delta. It's not that complicated.

Muthu
www.edison.co.in

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Well said, Lionel.
Consider two separate motors.
#1> 230 Volts @ 50Hz, Volts per Hz ratio = 230/50 = 4.6
#2> 400 Volts @ 50 Hz, Volts per Hz ratio = 400/50 = 8
Whichever motor you consider depends on whether you use a delta or wye connection.

With a delta connection and 100 Hz supplied by the VFD the motor is safe to apply 100Hz x V/Hz ratio 4.6 = 460 Volts.
The motor will still accept rated amps and will deliver rated torque, but at 100 Hz the motor will run at 6000 RPM.
The same torque and double the speed equals twice the HP.

With a wye connection you may apply 480 Volts @ 60 Hz directly to the motor.

With a VFD, you may wire the motor in delta and supply the VFD with 460 Volts. The VFD (properly configured) will supply the motor with 230 Volts at 50 Hz. With an input voltage of 460 Volts or 480 Volts, the VFD is also capable of supplying 460 volts at 100 Hz.

What are you going to use the motor for?
What speed range do you need?
What HP do you really need?
Can you work with a fixed speed of 3600 RPM?
If you can use 3600 RPM 480 Volts then you may not need a VFD.

("I was under the assumption if I had incoming power at 400VAC I can still use that to run the above motor configured in a DELTA configuration and the motor would see 230VAC as its supply voltage.") I understand that this is with a VFD supplied with 400 Volts, and outputting 230 Volts to the motor.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)
edison123,

With all due respect, I know I wasn't correct, hence the request for additional clarification.

After all, you replied..."regardless of frequency, a 400 V wye connection becomes a 230 V delta connection."

What does this even mean? How does a 400V Wye becomes a 230V Delta?

Perhaps may be if you had worded the above to say...if line voltage is 400VAC, then a Wye connection must be used and for a line voltage of 230VAC, a Delta connection must be used. Then I wouldn't have had to ask what might seem like a dumb question to you.

Cheers.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

colombo

With all due respect, you got more than what you paid for here. Your mistaken understanding of posts is your problem.

Muthu
www.edison.co.in

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)
Waross,

Thanks for the explanation. You are getting close to what I am trying to learn and understand.

Quote:


Consider two separate motors.
#1> 230 Volts @ 50Hz, Volts per Hz ratio = 230/50 = 4.6
#2> 400 Volts @ 50 Hz, Volts per Hz ratio = 400/50 = 8
Whichever motor you consider depends on whether you use a delta or wye connection.

With a delta connection and 100 Hz supplied by the VFD the motor is safe to apply 100Hz x V/Hz ratio 4.6 = 460 Volts.
The motor will still accept rated amps and will deliver rated torque, but at 100 Hz the motor will run at 6000 RPM.
The same torque and double the speed equals twice the HP.

So this implies that I must supply the motor #1 configured in a DELTA configuration with 460VAC at 100 Hz, and as long
I maintain the V/f ratio of 4.6 and it will have the same torque as if it was running at 3000RPM at 230VAC/50Hz?

So in theory, if this was a pump pumping 100gallons a minute at 3000RPM, it would now be pumping 200gallons a minute provided the impeller can withstand the increased RPM. Is that assumption correct or am I way off in my thinking?




RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Well yes but:

Quote (OP)

So in theory, if this was a pump pumping 100gallons a minute at 3000RPM, it would now be pumping 200gallons a minute provided the impeller can withstand the increased RPM. Is that assumption correct or am I way off in my thinking?
The load on the motor would now be 4 times what it was when it was pumping 100 GPM.
I would estimate the life of the motor to be under 5 minutes if the over-load protection didn't take it off line.
I am sure that Keith will agree that some would give it much less than 5 minutes. grin.
Really columbo7; If you want to know about motors, get a good book. An easy to understand short course is the Cowern Papers by Edward Cowern PE.
Cowern Papers
Also, as an industrial engineer, look at some manufacturers pump charts.
Many times you will see the same pump specs running at 1800 RPM and running at 3600 RPM.
You will quickly see a four to one ratio in motor size. When you compare a pump at 1800 to the same pump running at 3600 RPM the motor on the 3600 RPM pump will be four times the HP.

If you have a specific problem or application, give us the details up front instead of leading us around with guessing games.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)
Waross,

Thanks for the reply.

Quote:

If you have a specific problem or application, give us the details up front instead of leading us around with guessing games.

I do not have a specific problem per say (at least not yet), nor am I trying to lead anyone around with guessing games. Just trying to understand the operation of a specific system. I am not an electrical engineer so my questions may not be in line with what is common knowledge for you and your peers. All I am trying to do is trying to understand System X, that was running at a facility having 400VAC 50Hz power, to get it to run the same way at a Facility having 400VAC 60Hz.

For the time being, all the information that I have about this is a motor that is used in a Water pumping application. This is all the information that I have about the said motor and how it was controlled.

7.5Kw 230/400VAC D/Y 50Hz
Freq. Converter operation (S9) in DELTA connection up to 100Hz
7.5kW: 230VAC 3000 RPM at 50Hz
15kW: 460VAC 6000 RPM at 100Hz

So in one of your replies you stated.....

Quote:

With a delta connection and 100 Hz supplied by the VFD the motor is safe to apply 100Hz x V/Hz ratio 4.6 = 460 Volts.
The motor will still accept rated amps and will deliver rated torque, but at 100 Hz the motor will run at 6000 RPM.
The same torque and double the speed equals twice the HP.

In your last reply you stated....

Quote:

The load on the motor would now be 4 times what it was when it was pumping 100 GPM.
I would estimate the life of the motor to be under 5 minutes if the over-load protection didn't take it off line.
I am sure that Keith will agree that some would give it much less than 5 minutes. grin.

Please know that I am not trying to nit-pick nor find fault but rather trying to understand this. I am confused as to why would an OEM even bring up S9 mode operation for this motor at 460VAC 100Hz, if the said motor would die off after 5 minutes of operation?

I am simply trying to understand what the specified characteristics for this motor means in layman's terms. Thanks again for all your help and pointers. I am getting some of it, but still failing to see the Forrest from the trees.

Best regards.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Quote:


Does this mean I need 230VAC line power if I want to run this motor using the DELTA connection and 400VAC incoming line power to connect it using the Wye configuration? I was under the assumption if I had incoming power at 400VAC I can still use that to run the above motor configured in a DELTA configuration and the motor would see 230VAC as its supply voltage.

Regarding your last sentence...

With a VFD, you could. But the VFD created motor supply voltage wouldn't simply be 230V, it would vary in voltage and frequency as you started and stopped the motor and when you changed speeds.

Without a VFD, the motor connection has to match the incoming voltage, or to be more exact you need to make sure the V/Hz ratios of the motor and source match. Hence why 480V @ 60Hz could work as the source.

Read my and the other posts again since it was explained already. If you can't get that to connect then you need to get some books on the subject of using VFD's because this isn't a teaching site.

Bonus points to the person who correctly guesses why I setup the VFD to produce 460V@6.7Hz.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)

LionelHutz

Thanks for the help.

Just curious...

Quote:

this isn't a teaching site.

So if everybody here knows everything, what exactly is the purpose of this forum? I see people asking questions all the time on this section. It is more like 95% asking for some sort of help vs. Sharing new ideas.

Is there a disclaimer that I missed before i registered?

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Colombo7, Just to clarify -
# when you apply 400V to the motor with 'star' connected windings, what is the voltage across each of the phase windings: 230V (i.e. 400/sqrt3). Isn't it!
Now,
# when you apply 230V to motor with 'Delta' connected windings, the voltage across each of the phase windings is 230V.
What is important here is the voltage applied across the windings and that should remain constant (for a given frequency).
Hope the explanation is helpful.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

(OP)
Hi RRaghunath,

Thanks for the reply. I never thought of it in that that way (just didn't know the math involved until you pointed it out.) I've realized that I have got a lot of reading to do on the subject of Induction motors and 3 Phase AC in general. So with my limited to non existence knowledge on the subject matter, is it suffice to conclude from the information given so far that Delta connection is used for light duty tasks where as Wye connection is used for heavy duty tasks in simplistic terms? OR, do they do the same amount of work based on the available supply voltage at either 230 or 400 vac with the same motor configured either in Delta (for 230VAC) or in Wye (for 400VAC)?

Thanks again. Much appreciated.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Lionel; Was that set up as a torque motor to take up slack or was it inching operation.
Gee V/Hz = 0.01457, The rated voltage at 60 Hz = 4120 Volts
Probably inching a 4160 Volt motor for alignment. Too big for a torque motor.

columbo7 The thing is; when we ask the questions we understand the answers.
You have been lucky. We usually don't do this much teaching.
Many are bounced after the second or third post.
Be grateful for the help that you have been given.

p.s. Re the 100 Hz operation. that may be a trick more often used by compressor skid builders.
By running a motor at double voltage and double frequency, you double the HP.
This is sometimes done so as to use a smaller motor.
BUT
The manufacturer has to use a pump that will not overload the motor at 6000 RPM.
Yes, it can be done at the design stage, but you can not generally overspeed a centrifugal pump by very much.

And yes I have seen something similar done in a special case.
We needed a head of about 200 feet. The smallest pump capable of producing that head was much too large for the application.
The pump shop extrapolated a pump curve to find the RPM needed to develop the head required. They then calculated the HP required.
A suitable motor was selected and the pump was belt driven above the motor speed to get the 200 foot head.
That pump would normally have a motor of about 15 HP or 20 HP. At the increased speed, we needed 30 HP.
When you start talking about pump drives you must consider the pump as well as the motor.
Oh, and by the way, I haven't seen everything but 400 Volts @ 60 Hz is pretty rare in North America. What type of plant is this?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Bill - Yes, inching a ball mill.

colombo7 - OK, this isn't the site to get taught a complex subject from scratch. For example, you should have done some Google learning to know how wye vs delta worked.

Regarding your last question. By now you should already know:

- that the motor HP remains the same so the motor can do the same amount of work at either voltage.

- that the voltages need to be matched when the motor is directly connected to the source.

- that with a VFD you could use either voltage connection along with the matching source voltage to run the motor up to 50Hz.

- That the lower voltage connection using a higher voltage source allows the motor to run up to a higher frequency (and speed) that matches the source (using the V/Hz ratio) without losing motor torque.

Something not yet made clear is that you generally pick the higher voltage possible at the site for motor installs since a higher voltage lowers the current which makes the wiring and the equipment cheaper.

I haven't posted anything about the load because it could take another book or two to fully explain what various loads do as the speed changes.

RE: Can a motor rated for 460VAC 3-Phase 50Hz be used with 400VAC 3-Phase 60Hz Power

Hi Colombo7,

Here is an overview video about the differences between WYE and Delta : https://www.youtube.com/watch?v=3ktxtDW6UAE
Here is some Basic information about stepper motors: https://www.accu.co.uk/823-motors

We still don't know your application and I'm guessing that there might be a fan connected to the supply. Therefore, I'd like to mention that a decrease in power could have a detrimental affect on the performance of the fan system, which will cause your machinery to overheat.

Kind regards,

Zara






Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper - How ESI is Helping Move New Medical Device Product to Market Quicker & More Cost Effic
Early Supplier Involvement has long been a strategy employed by manufacturers to produce innovative products. Now, it almost seems like a necessity. Because decisions made in the design phase can positively affect product quality and costs, this can help add value to OEM bottom lines. This white paper will discuss many facets of ESI, including why it’s so valuable today, what challenges limit the benefits of ESI, how cost is impacted, and more. Download Now
White Paper - Moving to a Driverless Future
This white paper describes what we see as the best practices to support a sustainable engineering process for autonomous vehicle design. It exposes how to use simulation and testing in common frameworks to enable design exploration, verification and validation for the development of autonomous cars at a system, software and full-vehicle level to drive a mature product development process for automated driving. Download Now
Research Report - How Engineers are Using Remote Access
Remote access enables engineers to work from anywhere provided they have an internet connection. We surveyed our audience of engineers, designers and product managers to learn how they use remote access within their organizations. We wanted to know which industries have adopted remote access, which software they are using, and what features matter most. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close