Excel solution required : Calculation of sum of cells according to reference cell 1
Geosubhtech
Geotechnical
IE
Sir,
i want to calculate the overburden pressure at certain depth (reference C14) but including the effect of water table. As, below water table submerged density should be considered and above saturated density should be considered. So, i am looking for a formula which can calculate automatically the pressure by changing the water table depth (reference E1). Please see the attachments (spreadsheet and images)
Thank you.
[Sample image][1]
[sample image with cell formulas][2]
[Sample file][3]
[1]: [2]: [3]:
I can't do it all in one formula, but here's a method to do it with an additional column. You can change either the water table depth or the depth for the pressure to be calculated. I went quick so you should test before using too much.
 https://files.engineering.com/getfile.aspx?folder=42211c6f-0e4d-459f-94d6-a593a5ff775b&file=water_table_-_Modified.xlsx
it works fine. Thank you for the formulae. many many thanks