King Post wall

King Post wall

King Post wall

(OP)
I am doing a preliminary design of a king post wall. I have determined the overturning moment as normal for a 1m width section (into the page). The posts are spaced at 2m c/c. My question is, how do you account for post spacing?

For a 2m spacing, should I multiply the overturning moment by 2?

I’m thinking should I therefore multiply the restoring moment by 2? I don’t think this is correct? Soil arching has something got to do with it. For example if the wall is at 3m c/c each post is taking 3 times the 1m width moment due to the lagging in between. However the passive resistance is based on the arching effect of the embedded portion ?

I would appreciate a good reference. I have yet to come across a text book that provide a good design example on king post walls.

Thanks in advance

RE: King Post wall

Quote (ErieChch)

...how do you account for post spacing?

For a 2m spacing, should I multiply the overturning moment by 2?

Yes, multiply the overturning moment by 2.

The "secret" is to understanding what is happening is:

1. Assume the wall is infinitely long.

Then, for randomly placed backfill, any local effects like soil arching average out. Each post will have (more or less) the same force to resist.

2. Carefully select exactly what 2 meters (width) represents.

If the 2 meters (width) is centered on a single post, a sketch makes it clear that each post (on average) must support 2 meters (width) of backfill. This 2 meter assumed length (1 post + 1 meter of wall on each side of the post) repeats along the entire wall. This makes the the 2 meter width of wall the "tributary area" for loading of one post.

Corners or wall terminations are different... but at those locations, the wall details may be also.



www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

RE: King Post wall

(OP)
Thanks SRE - thats what i was assuming too. I have done a king post analysis in Wallap and followed the methodology provided and it works ok. I have had this checked by a senior engineer and he confirmed it. Wallap gave an embedment depth of 2.7m for 1.4m height with a Fos of 2.

However when doing a hand calc as a check, adopting the typical cantilever wall approach doesn't work as its not a continuous wall below the excavation line.

The Wallap method is to ignore the active thrust below excavation line due to soil arching (this is done by setting Ka to 0) and then to factor down the passive resistance as each post is only receiving its passive pressure from a 3d width of soil in front of the post. Kp is then factored to Kp (mod) which is Kp * (d * 3 / post spacing).
So for a Phi of 21 degress and a post hole width 0.5m, at 2m spacing, Kp = 2.11, and Kp (mod) = 2.11 * (0.5 * 3 / 2) = 1.58.

The above seems to work in Wallap but i cant get a hand calc to get an embedment depth/FoS thats in the ballpark.
Quick screen shot of some rough and ready calcs, hopefully not too hard to follow.

RE: King Post wall

What calculation method have you chosen in wallap? Unless you have selected piling handbook method your results will be off. Also the pressure calculation in wallap will give different results to hand calcs. Check wallap output to see by how much? I personally find cads piled wall suite easier by far for king posts if you have access to that?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close