Horizontal Reinforcement in CMU Retaining Wall Stem

Horizontal Reinforcement in CMU Retaining Wall Stem

Horizontal Reinforcement in CMU Retaining Wall Stem

(OP)
Im designing a cantilevered retaining wall and I am not sure if I should specify any horizontal reinforcement in the stem. Stem will be 8" CMU with No. 6 bars at 32" O.C. With standard masonry wall construction you have your horizontal wires usually at every other course with a tie-beam or bond beam at the top of the wall. I dont expect any lateral loads from the ends of the retaining wall; all the calcs check out for sliding, overturning, bearing, and stresses in the stem from the lateral soil loads. I didn't see anything in the ACI specifically for this either but I could be missing something. Any thoughts?

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

I'd include some horizontal reinforcing. You've got temperature and shrinkage stresses in the wall. Additionally, it's not realistic to expect your earth pressures to be uniform along the wall so some horizontal bending stresse ps will develop.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

(OP)
Ok that is what I figured. Do you think a bond beam with a bar in it at the top of the retaining wall is overkill? Their plans say they are going to put a chain link fence above this wall but I have a feeling they are going to at least put a wooden or nice vinyl fence on top because this is for a community with larger nicer homes. I added a surcharge on the retained side to account for this new load and any moments this fence may apply to the wall/footing. Do you think a bond beam at the top of the wall will help with the moments applied from the new fence?

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

What is the purpose of a "bond beam", when as a retaining wall, I assume the wall will be fully grouted? I would use smaller vertical bars at closer spacing, maybe #5-16, and say #4-16 horizontal. Using knockout blocks or H-blocks will facilitate full grouting. And don't forget waterproofing on the earth face if you want to prevent staining of the face.

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

2#4 @ 24 horiz

Mike McCann, PE, SE (WA)


RE: Horizontal Reinforcement in CMU Retaining Wall Stem

Mike,
Why would you use two in one course? That will just make fully grouting the wall more difficult.

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

I'd just use 9 ga dur-o-wal each second course... like a normal exterior masonry wall. You can use type S mortar due to exterior condition...

Dik

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

(OP)
No I i didn't design it to be fully grouted. Its going to be about 250 feet long so I figured that would be some good cost savings. Like I said above everything checks out from a calculation perspective but I didn't know if there was something else I was missing like shinkage, temps, industry standards, ect. that would require additional horizontal reinforcement.

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

I have never understood the concept of partial grouting. Where I am, contractors would charge you more, with all the fiddling around that is involved.

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

Don't forget control joints.....

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

Hokie: Done all the time here for bond beams in 8 inch CMU walls. Still have a net of 5" or so to play with for the grout too. Never had a problem.

And regarding fully grouted, I thought that being fully grouted was a requirement for any CMU below grade.

Mike McCann, PE, SE (WA)


RE: Horizontal Reinforcement in CMU Retaining Wall Stem

(OP)
Thanks for the heads up Mike! I looked up the building code and they require full grouting for CMU retaining walls.

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

Mike,
So if it is fully grouted, would you still group the bars, or distribute them?

RE: Horizontal Reinforcement in CMU Retaining Wall Stem

I would either distribute them horizontally, or bundle the bars in a vertical stack. I also specify avpeavgravel concrete infil.

Mike McCann, PE, SE (WA)


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close