Vent Stack Snuffing with CO2 extinguishing system???

Vent Stack Snuffing with CO2 extinguishing system???

Vent Stack Snuffing with CO2 extinguishing system???

(OP)
Hi,

Does anyone have experience in snuffing vent stack with CO2.
What are the design practices?
How to determine required CO2 capacity?
Any resources, philosophys?


Thank you inadvance,

Scyzoo
Replies continue below

Recommended for you

RE: Vent Stack Snuffing with CO2 extinguishing system???

A number of people seem to include CO2 snuffing for vents but I've not run across any design standards.  Perhaps others have.
The end result you're after is that you do not want to support a flame on the end of the vent.
Physically and mechanically you need to avoid details which will help to hold a flame, like recirculation zones and bluff bodies.  A clean deburred discharge would be preferred.
You can choose to extinguish an unwanted flame in a number of different ways with CO2.
- chemically, you need to add enough inert to prevent  flame propagation.  As a rough estimate of how much inert you need for this, calculate the gas air ratio of the lean limit mixture and replace the air with CO2.
- flame destabilization, flames become less stable as they become thermally leaner, so using the dilution techniqe above sometimes works even if you don't have enough gas to be technically enough, simply because a flame doesn't sustain as easily.
- starvation, adding the inert as a "plug" of CO2 in the vent flow so that it cuts off the flame's fuel source when the plug gets to the tip.  This needs a high pressure, rapid discharge flow of inert and is the technique used by some commercial vendors, like fire suppression system vendors. you could look at www.fenwalfire.com/products/index.htm
- mechanically, adding the inert as turbulent flow from a ring around the discharge is also used because it partially cuts off the flow of support air and also the inert velocity enhances the discharge velocity and helps in flame destabilization.
In practice, I suspect that satisfactory home made solutions tend to be a serendipitous amalgam of all of the above techniques.

David

RE: Vent Stack Snuffing with CO2 extinguishing system???

scyzoo,

you want to be careful with CO2 snuffing. It has triggered explosions/fire where the systems were not properly detailed.

Most plants rely on steam snuffing where it is compatable with the process. Flareman's cautions are well advised.


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close