Chemical Injection Point Orientation
Chemical Injection Point Orientation
(OP)
Hello every one,
We have field diesel distillation unit and we have plan to inject pour point chemical to heavy oil product ( Residual) which goes to crude tanks for storage. I have some concerns about injection point orientation.
As good practice we normaly inject the chemical on the top of the pipe but in our case only we have a drain fitting at lower position 6 clocks (6 inch pipe).
It is ok to carry out this job.
please see attached file (our Chemical Quill will be used)
Zayed
We have field diesel distillation unit and we have plan to inject pour point chemical to heavy oil product ( Residual) which goes to crude tanks for storage. I have some concerns about injection point orientation.
As good practice we normaly inject the chemical on the top of the pipe but in our case only we have a drain fitting at lower position 6 clocks (6 inch pipe).
It is ok to carry out this job.
please see attached file (our Chemical Quill will be used)
Zayed
RE: Chemical Injection Point Orientation
Top connections are preferred only for accessibility and maintenance reasons. Process wise, there is absolutely no difference.
The best thing to do is to provide injection point upstream of the pump or a control valve. Turbulence created across these devices will ensure proper mixing in all cases, regardless of the flow of main stream.
Dejan IVANOVIC
Process Engineer, MSChE
RE: Chemical Injection Point Orientation
RE: Chemical Injection Point Orientation
We decided to inject the chemical upstream residue pump after re-boiler (Heat exchanger residue /diesel) then after that will goes to 2 stages of exchangers( Crude/ Residue) finally will be stored to tanks.
Pipe specification 4 inch SS 316
Residue Tem 650 F and P=12 psi
Chemical type: Pour point (wax based & will be diluted with Naphtha DF=2)
Any concerns (Process, Corrosion....etc) will be raised gentlemen
Zayed
RE: Chemical Injection Point Orientation
I have seen so many pipe failures over the years because of failed quills that I don't count them any more.
A short piece of alloy 625 is cheap compared to a failure.
= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, Plymouth Tube
RE: Chemical Injection Point Orientation
RE: Chemical Injection Point Orientation
Our Quill is made from 316L SS; the rated Temperature (550 C to 800 C) is above the residue Temperature. Also system pressure is very low. Galvanic corrosion is not applicable (316 pipe and 316L), the question here what/why the failure will be occurred as such system.
Zayed
RE: Chemical Injection Point Orientation
It is stronger (especially at temperature), more corrosion resistant, and more erosion resistant.
I have seen quills fail in fatigue, corrosion , erosion, and mechanical damage (large debris). Once they fail the chemical being injected washes along the pipe wall and often causes corrosion issues there because it is concentrated.
= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, Plymouth Tube
RE: Chemical Injection Point Orientation
To make the chemical injection on top side of the pipe is the good choice. If you didnĀ“t chose this option after some time of operation the scale will plug your injection quill.
good luck
Luis Marques
RE: Chemical Injection Point Orientation
If you are dealing with a chemical injection, for naphtenic acid protection, alloy 625 is a good option. To avoid tubulance and corrosion your quill should be injecting the chemical into a 12" pipe.
Good luck
Luis Marques
RE: Chemical Injection Point Orientation