If the Pipe is carbon steel. Anything wrong if I use a SST thermowell?

If the Pipe is carbon steel. Anything wrong if I use a SST thermowell?

If the Pipe is carbon steel. Anything wrong if I use a SST thermowell?

(OP)
If the Pipe is carbon steel. Anything wrong if I use a SST thermowell? Or do I have to get a carbon steel thermowell to match it?
Replies continue below

Recommended for you

RE: If the Pipe is carbon steel. Anything wrong if I use a SST thermowell?

It all depends on what's going through the pipe. There are services where carbon steel is perfectly suitable that you really don't want to use an austenitic stainless steel...

RE: If the Pipe is carbon steel. Anything wrong if I use a SST thermowell?

Not enough information. There could be concerns with thermal differential and corrosion. Frankly, I would stay away from dissimilar materials when at all possible.

RE: If the Pipe is carbon steel. Anything wrong if I use a SST thermowell?

Tell us about the service and we will tell you about the pros and cons.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, Plymouth Tube

RE: If the Pipe is carbon steel. Anything wrong if I use a SST thermowell?

Sst is also less thermally conductive. The only time I'd use a SST thermo well in a carbon steel line is if NPT threads were permitted- then it's just a matter of convenience, as corrosion probably isn't a big risk ( or the threads themselves would be an issue)

RE: If the Pipe is carbon steel. Anything wrong if I use a SST thermowell?

SST thermowells are often used in carbon steel pipe and many times wrongly so. As the other responders have stated, it depends on the service conditions.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close