motor amps / pump power

motor amps / pump power

motor amps / pump power

(OP)
Hi,

I was wondering if it is necessary to subtract no load amps from measured amps of a motor/ pump combination to determine pump hp draw in the following formula:

HP = (1.73 x amps x voltage x P.F. x eff.)/746

Thanks,
Stan K.

RE: motor amps / pump power

No

RE: motor amps / pump power

(OP)
Why?

RE: motor amps / pump power

As an approximation, the current is the vector sum of an inductive magnetizing component (Inoload= no-load current) and a resistive load component (Iload).
Itot=Iload + j*Inoload

For powers near to nameplate power for high-speed motors, the ratio of actual current to nameplate current is reasonable approximation of the fraction of full load, since Inoload will be somewhat less than Iload and it’s contribution is reduced even further by the vector addition.

At lower powers, or for lower-speed motors, the magnetizing component becomes more significant.   If we want a more exact solution, we can estimate:
Iload=sqrt(Itot^2-Inoload^2)
P = Iload/Iload100 = sqrt (Itot^2-Inoload^2)/Iload100
  where P is the fraction of full power
  Iload100~Inameplate but more exactly  Iload100=sqrt (Inameplate^2-Inoload^2)

we have neglected changes in power factor, and efficiency.

RE: motor amps / pump power

Also we neglected leakage reactances in the equivalent circuit.

RE: motor amps / pump power

Are you trying to figure the actual HP less the drag of the seal and others that are adding to the total?

RE: motor amps / pump power

Steve - I'm not sure if your question is directed at me or the original poster. I'll assume it's directed at me:

I was determining the power associated with the load branch of the equivalent circuit. That would include shaft output plus friction plus rotor losses, and definitely not core losses. (Stator losses and stray losses are a little muddier to associated with a branch in this model).  For simplicity I'd like to think of them as output power.

The reason that we cannot always predict output load based on the ratio of no-load current to FLA becomes obvious by looking at an unloaded motor which can draw 20%-60% of full load current under no-load conditions (toward the low end for high-speed motros and towrad the high end for low-speed motors).  Let's say I measure 30% of FLA when uncoupled... clearly I am not operating at 30% of output power.  That points out the need to correct the calculation by vector subtraction to remove the effect of the inductive no-load current.

Forgive me if I have misunderstood your question or told you what you already knew.

RE: motor amps / pump power

My mistake Pete, It was for Stan. I asked that question since he asked "why" and figured he was trying to exclude any other variables that add to the motors load and gives him a less than accurate picture of what the pump is actually doing. Especially if he is plotting the HP vs GPM on a curve and nothing adds up the way it should.

RE: motor amps / pump power

if all you are trying to do is a load test at the site, i have seen it done using a watt-hour-meter.

RE: motor amps / pump power

motorman's comment reminds me that the most straightforward way to determine real power input is an instrument which measures phase angle between voltage and current. That is a much more direct and precise method than the approximate method I identified above.

I guess that if a watt-hour meter is available, then it can serve the same function (divide watt-hours by measurment time to determine watts).  Good point.

RE: motor amps / pump power

Suggestion to stankap (Mechanical) Aug 5, 2002 marked ///\\\
I was wondering if it is necessary to subtract no load amps from measured amps of a motor/ pump combination
///No.\\\
 to determine pump hp draw in the following formula:

HP = (1.73 x amps x voltage x P.F. x eff.)/746
///Please, notice that the efficiency and power factor take care of that since they are both smaller than one. However, there are relationships or equations that lead to the HP determination over the mechanical power delivered to rotor over the motor air gap. They are essentially used in textbooks to explain the motor functioning or principles, only. E.g.
Pmech=nu x Re[p x ms x Ir' x Ems* / (2 x ws)], in Watts
nu .. rotor speed in rad/sec
ws=2 x pi x f .. stator angular synchronous frequency in rad/sec
f .. frequency in Hz, e.g. 60Hz
p .. number of poles
ms .. number of stator phases
Ir' .. rotor current transferred to the stator side in Amps
Ems* .. complex conjugate (phasor) of internal stator voltage
Then, 1HP = 746 Watts converts the Pmech to HP.\\\

RE: motor amps / pump power

I guess I never read the question carefully. IF power factor is known (it appears that is the case in the original question), THEN there is no need to subtract no-load current.

Quite often only current is known. That is the situation I addressed in my 8/5/ message.

Sorry for the confusion.

RE: motor amps / pump power

(OP)
Thanks Guys
Stan K.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close