650 Tank
650 Tank
(OP)
Dear Friends,
Contractor has hydrotested a storage tank built to API 650.
It is noticed that some tank settlement has taken place at the edges and at different points in the bottom floor.
What are the acceptable limits for different types of tank settlements and please advise which code / standard provides these limits.
Please note that tank has not been put into service and contractor has not formally handed over the tank to owner.
Thanks in advance.
Contractor has hydrotested a storage tank built to API 650.
It is noticed that some tank settlement has taken place at the edges and at different points in the bottom floor.
What are the acceptable limits for different types of tank settlements and please advise which code / standard provides these limits.
Please note that tank has not been put into service and contractor has not formally handed over the tank to owner.
Thanks in advance.
RE: 650 Tank
RE: 650 Tank
653-2005 Section 12.5 Measured Settlement during hydrostatic testing provides the requirements for the initial survey and the evaluation for acceptance per Appendix B.
If the settlement is beyond that specified then the contractor should provide you with a design analysis which indicates that it is safe to put the tank in operation.