It seems to be a contradiction in the requirement of draft curtains between IBC and codes.
IBC 2006 states the requirement of draft curtains in 910.3.5 and table 910.3. So, a high-piled Group S-1 with type III commodity, area =30,000 ft2 and no ESFR sprinklers (only normal ones)will require draft curtains (either option 1 or 2) because the table gives maximum area formed by curtains.
IFC 2006 Table 2306.2 states that for the same condition, draft curtains are not required.
Am I reading the codes wrong or there is a contradiction?
Thanks
IBC 2006 states the requirement of draft curtains in 910.3.5 and table 910.3. So, a high-piled Group S-1 with type III commodity, area =30,000 ft2 and no ESFR sprinklers (only normal ones)will require draft curtains (either option 1 or 2) because the table gives maximum area formed by curtains.
IFC 2006 Table 2306.2 states that for the same condition, draft curtains are not required.
Am I reading the codes wrong or there is a contradiction?
Thanks
RE: Contradiction in the use of draft curtains (IBC, IFC) ?
I seem to recall down this journey of the pellet storage building that you will not have high-piled combustible storage. You don't need draft curtains because your maximum building area is below the 50,000 square foot area threshold between each draft curtain.
RE: Contradiction in the use of draft curtains (IBC, IFC) ?
I follow IBC and in 910.3.5 it says: "Where required by Table 910.3, draft curtains shall be provided in accordance with this section". In my view, this paragraph is saying that the Table 910.3 determines when to use draft curtains.
For my particular case, High-piled storage, Class III (storage height=40 ft), the table shows minimum draft curtain depth 6 ft (Option 1) and maximum area formed by draft curtain = 8,000 ft. This means that my building (30,000 ft2) does need draft curtains per IBC. Note that my building is S-1 and high-piled storage, so my understanding is that I have to satisfy BOTH requirements in the Table and not only S-1.
And there is were I see the contradiction with IFC Table 2306.2 which for a 30,000 ft2 building, for high-piled storage, class III commodity does not require draft curtains.
Please help me to clarify this issue.
RE: Contradiction in the use of draft curtains (IBC, IFC) ?
Note that IFC Table 2306.2 does not require draft curtains when the building is equipped with an appropriately designed fire sprinkler system, or is Class I-IV less than 2,500 or high hazard less than 500 square feet - high piled storage area.
However; the IFC/ [F] IBC Section 910.2.1 still requires draft curtains at 50,000 sq ft, regardless of use (high piled storage or other use). Both tables are required to determine application to high piled storage.
stookeyfpe is correct, there is no conflict.
However, both tables must be used to determine high piled storage requirements. It might be helpful if a footnote was added directing IBC users to IFC Table 2306.2 for high piled storage draft curtain requrements.
RE: Contradiction in the use of draft curtains (IBC, IFC) ?
Thank you all