It seems to be a contradiction in the requirement of draft curtains between IBC and codes.
IBC 2006 states the requirement of draft curtains in 910.3.5 and table 910.3. So, a high-piled Group S-1 with type III commodity, area =30,000 ft2 and no ESFR sprinklers (only normal ones)will require draft curtains (either option 1 or 2) because the table gives maximum area formed by curtains.
IFC 2006 Table 2306.2 states that for the same condition, draft curtains are not required.
Am I reading the codes wrong or there is a contradiction?
Thanks