I am working on a job where the electrical contractor pulled unshielded, twisted pair Cat 5 cable for RS485 communications. I know RS485 is usually run in shielded twisted pair, and I am wondering if this will work. The runs are all in dedicated metal conduit, which I think would function as a shield. Some of the runs are long, ~400'
Thanks,
John
Thanks,
John
RE: RS485 in Unshielded Cable
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
RE: RS485 in Unshielded Cable
http://www.edn.com/archives/1996/080196/16df5.htm
David Baird
Sr Controls Designer
EET degree.
Journeyman Electrician.
RE: RS485 in Unshielded Cable
The dedicated conduit is great.
What are the 485 devices? Just one on either end correct?
Hopefully the devices are edge limited or controlled.
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: RS485 in Unshielded Cable
It's really new for me. We always request shield twisted pair cable for RS485, it's also recommend at all manuals ( of corse what I know). More then this, we always design ground connection to the shield ( for example: only one end of shiels is grounded).
But, I'm sure you have good expirience w/o too. Nice know.
Regards.
Slava
RE: RS485 in Unshielded Cable
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
RE: RS485 in Unshielded Cable
Many times I have used unshielded for temporary instrumentation, "grabbing what I have", and had no issues either.
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: RS485 in Unshielded Cable
Shielded cable is better, and certainly recommended, but RS-485 is a differential signal so it is more robust than a signal referenced to ground like RS-232.
RE: RS485 in Unshielded Cable
Thanks,
John
RE: RS485 in Unshielded Cable
Look at Ethernet, 1Gb/s and no shielding. Look at your DSL 10,000ft+ 2~3Mb/s no shielding. Granted these examples have a robust comm protocol. Hopefully the instruments are designed correctly.
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: RS485 in Unshielded Cable
RE: RS485 in Unshielded Cable
RE: RS485 in Unshielded Cable
Ethernet has an electrical isolation through its transformers. It is not the case with RS485.
This is what makes Ethernet so solid, and so popular in the telecom world where whole CPU racks are made from multiple CPU cards talking to each other through their Ethernet port, instead of through a system backplane.
RE: RS485 in Unshielded Cable
I think Slava is right as the twisted pair has to be shielded [screened].
First of all the Cat 5 cable type is obsolete and Cat 5 e is instead now.
Second, if the insulation is PVC and the conduit pass through manhole, the cable is exposed for 5-8 ft and water will penetrate between conductors. The capacity will rise and it will spoil all good performances sooner or later.
Third, the cables are still limited to a maximum of 100 m (328 ft) in length (normal practice is to limit fixed ("horizontal") cables to 90 m to allow for up to 5 m of patch cable at each end).
So, if the total length is about 400 ft the pair has to be shielded at least.
Best Regards
RE: RS485 in Unshielded Cable
I have never heard of PVC suffering from water penetration problems before. XLPE suffers from this problem, which is why XLPE insulated cables are almost always sheathed in PVC. Some confusion?
Also the 100m limit applies to Cat 5 cable operating under 100BaseT conditions - using a relatively low frequency transmission such as RS485 won't have the same problems, although loop impedance might become problematic over a very long run.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: RS485 in Unshielded Cable
With all due respect you are wrong, sir!
First of all the jacket is made of PVC –power cables mainly- due to other properties of PVC as mechanical resistance and flexibility-but there are other materials as hypalon, chloroprene[neoprene] , fire-resistant non-halogeneted materials and other. The XLPE insulated core has no problem with humidity for low and medium voltage cable.
For high-voltage cable, longitudinal and transversal water barrier [moisture barrier] is provided. PVC moisture resistance is low-not so low as polyamide [nylon] but still low.
Also the permittivity factor is high[ 7-10] and the tang.delta too. This material is indicated nor for telecommunication cable as dielectric attenuation is high neither for medium voltage cable.
In the old good time the telecommunication cable core was paper insulated and lead sheathed. All the electrical properties as capacity and capacity unbalance was very good and for long time.This cable was very expensive .So the polymer used to be employed instead.No cable –for long and medium distance –was insulated with PVC except switchboard cable-short length and in dry location.For outside location the cable was insulated with LDPE[Low Density Polyethene] namely foam[cellular]and as the PVC jacket was not moisture barrier a sort of Petroleum Jelly used to fill the air gap between core and jacket.After a while, a moisture barrier of longitudinal applied aluminium foil, both side poliethene covered was employed, so PJ was not required yet and the core was insulated with solid HDPE[high density poliethene-as LDPE seems to be carcinogene].Up today telecommunication cable insulated PVC is limited for dry location and limited length.
By the way, the signal attenuation for 100 Khz or 1000 Khz does not seems to differ.
Best Regards
RE: RS485 in Unshielded Cable
Seems we both may have some errors then....
Expand a little on this statement: "Second, if the insulation is PVC and the conduit pass through manhole, the cable is exposed for 5-8 ft and water will penetrate between conductors." How will this occur? Water penetration of PVC sheathed cables doesn't take place to any practical level. If PVC allowed water to penetrate the cable to any significant level, why would cables designed for service in wet environments be sheathed in PVC?
Signal attenuation? I don't disagree. I do wonder why you think there is a 100m limit when using the cable with RS485. The spec for 100BaseT permits 100m over a Cat5 cable. I don't think there is a published standard for distance using RS485 over Cat5 cable, but if there is feel free to post a link to it. RS485 can run up to about 1200m with appropriate cable. I doubt that this would be achievable with Cat5, but to imply that there is a 100m length restriction using RS485 over Cat5 based on the limitations of 100BaseT over the same cable is more than a little dubious.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: RS485 in Unshielded Cable
I agree with you is no standard where the length of cable for RS485 is limited to 100 m. But Cat 5/5e cable performance characteristics and test methods are defined in TIA/EIA-568-B.2-2001.I have not this standard now, but - if I well remember-there is somewhere stated the maximum length. I am sure it is possible to use it for a longer distance even the signal amplitude is under the value required by this standard but still tolerable, as you said.
I don't agree with you about using PVC jacket in wet location. Only PVC jacket does not avoid water penetration into the cable. We need a moisture barrier as aluminum foil and/or polyester wrapping over the core assembly, under the jacket.
For example, see
http://www.jembo.com/public/product.php?type=26
I agree with you the water penetration depends on water level in the ground.But if a manhole is involved, no matter how dip the ground water level is, the manhole will be full of water for a while or for ever.
Best Regards
RE: RS485 in Unshielded Cable
As Scotty mentioned earlier, those length limits you mention are based upon a high baudrate 100BaseT signal... at the baudrates 485 is running, you won't have nearly the same issues with signal integrity. Capacitance (the biggest killer here) and inductance will be less of an issue at the slower rates. Therefore, you're going to get significantly longer distances out of the Cat5 cable than 100m.
Dan - Owner

http://www.Hi-TecDesigns.com
RE: RS485 in Unshielded Cable
RE: RS485 in Unshielded Cable
RE: RS485 in Unshielded Cable
Of course it's depend on the application, in lot of cases, today, for avoid all such " problems" we used RS485 to FO convertrs. FO and convertors are so cheapper.
Regards.
Slava
RE: RS485 in Unshielded Cable
My hate in front of PVC and mainly against Cat 5 has a long history. A long time ago I designed a web of 400-500 ductbanks c/w manholes for a fossil fired power station.
Through this web I routed about 30 pair cables –I am not sure if they were really cat5 but very similar-for a distance of 2000 ft[or more].I don't remember what frequency was the carrier [may be 100kHz].At the beginning –let say 2-5 years – all the system worked excellently. And suddenly all it was changed. The signal was jammed and the system lost its stability.
So I checked the routing. First of all the manholes were full of water. The dedicated steel duct for instrument cables was partial used for power cables –on a fragment was even a medium voltage shielded cable. The end patch was deployed from the original place and so on. We decided to substitute all these cable for a screened [shielded] pairs cables. After then no trouble of this kind was noted.
But as ScottyUK said may be was a change in carrier frequency and the 100Khz was not from the beginning. Never the less the shielded pair mended the outage.
RE: RS485 in Unshielded Cable
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: RS485 in Unshielded Cable
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: RS485 in Unshielded Cable
Dan - Owner

http://www.Hi-TecDesigns.com
RE: RS485 in Unshielded Cable
We left the 4 unused wires tied to GND to get a partial shielding. As stated before, twisted pair has a better common-mode noise balance on both wires, so we just left 100ohm shunt resistors at both ends for cable impedance matching, along with zeners and ceramic caps in parallel, to sink some line noise. All data was Manchester encoded to prevent loading lines (like Ethernet), and the bitrate was chosen low to stay away from any resonance.