I have designed several tilt-up panels,mostly by hand. Lately we have bought PCA WALL and I love it. It can do a second order analysis which is a must for heavy loads and thin panels. Make sure that the effective moment of inertia is correctly specified for heavy gravity loads. According to ACI, for columns, effective I of 0.4 Ig can be used. Then you have to divide it with Beta d also. The bottom line is that a value of 0.25 Ig should preferably be used for heavy gravity loads. Wind load deflection can be checked for I eff calculated on the basis of wind loads. PCA Wall is particularly good when there are a lot of wall openings. As for ENERCALC, I like to check the numbers calculated by that program with hand.