design of busbars

design of busbars

design of busbars

(OP)
Please design a copper bus bar system for an enclosure of 2 x 1.8 x 1 mtr. The current rating of the bus is 7000 A rms at 415 V for 180 secs. Thereafter the current is 1600 A rms continuous at the same voltage.
While 7000 A is being passed the bus bar should be within permissible temperature limite. The temp permitted at 1600 A is 80 deg C. (40 + ambient 40)
I only need to know the cross section of conductor needed. No other details are required.
Exact calculation is required.
Regards
Hari Haran Rajgopal

RE: design of busbars

Hi,

I might suggest that you pose this question on the Electrical Power Engineering it seems more like their sort of question.

Any help ?, yes no let me know.

Regards

RE: design of busbars

Try this rule of thumb, 1000 amps per square inch for copper, 700 amps per square inch for aluminum bus bar.

RE: design of busbars

Sounds like a college homework to me...

anyway, you can use 1 sq. inch of copper carries 1000 amps..
..the resistivity of a pure copper is ...10.2 at 32 degF ..also,

this might help too..

Area of a circle = 0.785(dxd) cir mils where d is the diameter in cir. mils

In square measure,

Area of cir mils = 0.785x1x1 =0.785 sq. mils

Cir mils =0.785d squared/ 0.785 = d squared

good luck
dydt

 

RE: design of busbars

Visit www.powellelectric.com, click on the "Technical Briefs" section, and read PTB #24.  Basically the only way to be sure of the sizing is by performing actual heat rise tests.  1000 A/in^2 is not a practical way to design.  The current densities of bus bars used in PowlVac metal-clad switchgear range from 500 to 1200 A/in^2 for identical 60 C temperature rises for 1200 A to 3000 A continuous current bus bars.

RE: design of busbars

Suggestion: Check the more officical documentation: Standards, e.g.
1. NEMA BU-1 Busways
2. NEMA BU-1.1 General Instruction for Proper Handling, Installation,
Operation, and Maintenance of Busways Rated 600 Volts or Less
3. UL Std 857 Electric Busways and Associated Fittings
4. ANSI/IEEE C37.20 Switchgear Assemblies Including Metal-Enclosed Bus
5. ANSI/IEEE C37.23 IEEE Standard for Metal-Enclosed Bus and Calculating Losses in Isolated-Phase Bus
6. ANSI/NFPA 70 National Electrical Code
7. Visit
http://busbar.copper.org/ampacity/busbar.htm
8. Search this Forum. There are some excellent postings already

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close