design of busbars
HariharanRajgopal
3
Please design a copper bus bar system for an enclosure of 2 x 1.8 x 1 mtr. The current rating of the bus is 7000 A rms at 415 V for 180 secs. Thereafter the current is 1600 A rms continuous at the same voltage.
While 7000 A is being passed the bus bar should be within permissible temperature limite. The temp permitted at 1600 A is 80 deg C. (40 + ambient 40)
I only need to know the cross section of conductor needed. No other details are required.
Exact calculation is required.
Hari Haran Rajgopal
I might suggest that you pose this question on the Electrical Power Engineering it seems more like their sort of question.
Any help ?, yes no let me know.
Try this rule of thumb, 1000 amps per square inch for copper, 700 amps per square inch for aluminum bus bar.
Sounds like a college homework to me...
anyway, you can use 1 sq. inch of copper carries 1000 amps..
..the resistivity of a pure copper is ...10.2 at 32 degF ..also,
this might help too..
Area of a circle = 0.785(dxd) cir mils where d is the diameter in cir. mils
In square measure,
Area of cir mils = 0.785x1x1 =0.785 sq. mils
Cir mils =0.785d squared/ 0.785 = d squared
good luck
dydt
Visit click on the "Technical Briefs" section, and read PTB #24. Basically the only way to be sure of the sizing is by performing actual heat rise tests. 1000 A/in^2 is not a practical way to design. The current densities of bus bars used in PowlVac metal-clad switchgear range from 500 to 1200 A/in^2 for identical 60 C temperature rises for 1200 A to 3000 A continuous current bus bars.
Suggestion: Check the more officical documentation: Standards, e.g.
1. NEMA BU-1 Busways
2. NEMA BU-1.1 General Instruction for Proper Handling, Installation,
Operation, and Maintenance of Busways Rated 600 Volts or Less
3. UL Std 857 Electric Busways and Associated Fittings
4. ANSI/IEEE C37.20 Switchgear Assemblies Including Metal-Enclosed Bus
5. ANSI/IEEE C37.23 IEEE Standard for Metal-Enclosed Bus and Calculating Losses in Isolated-Phase Bus
6. ANSI/NFPA 70 National Electrical Code
7. Visit
8. Search this Forum. There are some excellent postings already