Eng-Tips is the largest forum for Engineering Professionals on the Internet.

Members share and learn making Eng-Tips Forums the best source of engineering information on the Internet!

  • Congratulations JStephen on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

etap showing FCT not determined error on busbars and OCPD's

Status
Not open for further replies.

@Ankita

Electrical
Joined
Dec 12, 2024
Messages
3
We're designing one of client's SLD in etap but every time we run the Short circuit, all the busbars and OCPD's are not able to calculate the Fault clearing time and it's showing FCT Not Determined error. Is anyone else facing the same issue or aware about the appropriate settings that can help resolve this error. Attached is the screenshot for the exact errors.1733977587322.png
 
Hello,

You have to make the relay settings and (or) provide the correct fault clearing time in ETAP.
 
That relay settings will still be applicable only for the electronic trip breakers. But we're getting this error on the thermal magnetic fixed trip breakers as well.
 
You have to enter the fault clearing time for the thermal magnetic breakers as well
 
How can we calculate the Fault clearing time for the breakers or is there some reference from where we can get these values? Please confirm.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top