There is a pipe penetration thru platform grating. Is toe plate required for this penetration? What are OSHA's requirements for toe plate in this case?
Thanks,

Ibro V.
 
I think that the purpose of a toe plate is to keep objects from falling through the hole as well as keep people from slipping under the mid-rail. If the opening between the grating and the pipe is small enough you should be OK without a toe plate. How large is the pipe and how large is the opening?
 
I would use banding on the grating. Also, as stated above, I would keep the gaps to minimum. A general rule that I used for many years is the COKE bottle (2 inch diameter sphere) should be able to fall through any gap.

Good luck


Regards,
Lutfi
 
Here is what we follow:

For pipe penetration requring 6" dia clear opening or greater, use a 1/4" thick, 6" high collar band. For smaller openings weld a 1/4"x4 1/2" gelvanized checker plate split ring (horizontally)to the grating (around the pipe).
 