1-phase electricity supply to 3-phase motor
1-phase electricity supply to 3-phase motor
(OP)
We have only single-phase generator for emergency back-up, but we got 3-phase load (mainly water pump and air-con compressor). If we loop R-Y-B together and feed supply by single-phase generator. What will be the possible impact to 3-phase motor.
RE: 1-phase electricity supply to 3-phase motor
RE: 1-phase electricity supply to 3-phase motor
Some validation of my locked rotor current comment would be appreciated.
RE: 1-phase electricity supply to 3-phase motor
If it's a wye-wound three-phase motor then no current will flow unless you hook up a ground to the neutral.
That part was probably an obvious unstated assumption.
Definitely won't start rotate (although if you started it rotating with external force it might concievably stay rotating similar to single-phase motor).
I believe it's possible that it might draw slightly lower current than a locked rotor current.
The flux path is much different. In normal 3-phase we have flux from one pole group a,b',c acting together with max mmf equal to 1.5 times that of a single pole-phase group(i.e. a) and returning through adjacent pole phase groups a',b,c' on either side.
In single phase configuration, the max flux is smaller (1 times instead of 1.5 times) but the turns per phase remain the same.
Also the flux path length within iron is much shorter (a returns through adjacent pole-phase groups b' and c' which is 1/3 the normal circumferential length of the flux path) but air gap length remains the same.
Both of the above would likely have an effect on the inductances associated with equivalent circuit parameters Xm, X1, X2.
Also the stator now acts as if it had 3 times as many poles as before. Rotor frequency is three times higher. I believe this factor would increase X2 and possibly R2 for large motors (where skin effect is an important factor in rotor resistance).
Altogether it's a mixed bag of effects. I'm not sure which will predominate. Since in a normal motor the series reactances X1 and X2 are the primary factors determinng
LRA ~ V/(X1 +X2), it seems reasonable that the increase in X2 due to increased rotor frequency might be the most dominant effect, resulting in somewhat lower current than LRC.
Just a guess. Any more thoughts?
RE: 1-phase electricity supply to 3-phase motor
RE: 1-phase electricity supply to 3-phase motor
RE: 1-phase electricity supply to 3-phase motor
electric pete , where do you find this data??? I figured it wouldn't turn but I'm in awe again.
Now to be serious. It may sound silly but why connect the 3 phase loads to the standby system at all. It's allways been the problem that emergency or standby systems are overloaded by 600% and shut down 2cycles after the mains~ so getting these off the system would be the go. If firewater and smoke extraction / ventilation are required then get a back up for them.
As gordonl suggests trip the non essentials. generally we connect the control cct to an unsupported phase or circuit - not connected to the essential services system.
Regards
Don
RE: 1-phase electricity supply to 3-phase motor
phase converter in your future. It could save you
a lot of wireing headaches.
RE: 1-phase electricity supply to 3-phase motor
RE: 1-phase electricity supply to 3-phase motor
RE: 1-phase electricity supply to 3-phase motor
RE: 1-phase electricity supply to 3-phase motor
RE: 1-phase electricity supply to 3-phase motor
Visit
http://www.thomasregister.com
and type Converters: AC to AC under Product or Service which will return 44 companies to inquire about 1 phase to 3 phase converters.
Also, search web sites, e.g.
http://www.phaseconverter.com/static-converter.html