Instantaneous Trip => Rule out mechanical causes
2

Instantaneous Trip => Rule out mechanical causes

Instantaneous Trip => Rule out mechanical causes

(OP)
We had an 800hp motor associated with a radial-flow centrifugal pump trip on instantaneous current. The instantaneous trip is set well above locked rotor amps (verified as-found setting afterwards).  

It was suggested that the cause of the trip may have been the abnormal fluid system lineup which allowed additional flow through the pump during start may have been the cause.

My viewpoint is that if motor has tripped on instantaneous (and setting verified well bove LRA), then we should be able to rule out all mechanical causes.  Do you agree?  My reasoning would be as follows:

Anything that places extra mechanical load on the shaft (up to an including a seized-shaft due to bearing failure) should increase the time duration that locked rotor current id drawn, but not the magnitude of the current. So these types of mechanical problems should cause a time-overcurrent trip, not an instantaneous trip.  

Do you agree that mechancial causes can automatically be ruled out if motor trips on instantaneous (vs time overcurrent).

RE: Instantaneous Trip => Rule out mechanical causes

2
electricpete -
I concur that the worst case mechanical failure by definition is a locked rotor, which the motor is rated to withstand for a stated period of time.  Any current in excess of the locked rotor value MUST be due to an electrical fault condition.  
Was there any evidence of such a fault?  What about a relay oscillogram - any info from that quarter?  (Perhaps you could post an oscillogram as you did for your previous motor starting post)
Just a thought - you say that the instantaneous is set well above the locked rotor, but does the setting allow for full offset in the locked rotor current waveform?  

RE: Instantaneous Trip => Rule out mechanical causes

(OP)
peterb good discussion - In this case the instantaneous function is set for 1.4*LRA.  But it's an electronic relay which incoporates an inverse characteristic for the instantaneous element (sound like a contradiction but it's not) for times less than about 0.1 sec.  The intent of that inverse characteristic is to mimic the shape of ac plus decaying offset so that the instantaneous "asymptote" can be set closer to LRA.  Manufacturer literature originally recommended setting at 1.1*LRA... we went to 1.4LRA for extra margin against spurious trips. Our total peak current including dc offset is higher than the asymptote of the instantaneous trip but well within the curve published by the manufacturer. This makes me a little skeptical because we test only the asymptote portion of the instantaneous feature... too difficult to test the inverse portion.  So in order to prevent tripping, we are "relying" on a portion of the curve that we don't test.  Mfr now is hedging a little bit... suggests that we should bump our setpoint if we're seeing trips. This is first trip in 10 yrs among 6 similar motors started approx once per month.  There are a number of reasons to expect possible variability in instantaneous performance.
These would include phase closing angle, motor residual magnetism (although I've never heard of this as a factor except possibly after dc testing).  

Motor, relay, cables, everything checked fine (only abnormal thing was mechancial system lineup). Relay was double-checked by vendor.

The only things that were slightly different during this particular start was the ac power supply lineup and the mechanical fluid system lineup (which I believe to be irrelevant as discussed).

Regarding the power supply lineup:
#1 -  Voltage was in fact being monitored and was lower than normal (should reduce starting current).  
#2 - with equipment powered from different sources we might possibly  expect somewhat different R/X ratio (dc decay) depending on the source?  

RE: Instantaneous Trip => Rule out mechanical causes

Suggestion: When it comes to a peculiar situation like this, one should not rule out the relay or protective device malfunction, unless one is biased in favor of motors.

RE: Instantaneous Trip => Rule out mechanical causes

(OP)
jbartsos - relays tested ok when tested both on-site and by the vendor. (see 2nd paragraph 8/21 post). That is to say the instantaneous element picked up when a current slightly greater than the asymptote was applied.  

It is one of those non-reproducible things that makes you rack your brains. The oscillographs posted on the other thread are of this exact motor, on a subsequent test start (started normally).  Unfortunately, there was no permanently-mounted oscillography (or digital relays) to capture this one-time event.

It is of significance because the sole purpose of this pump is to auto-start in order to fulfill it's plant safety-function.  If it trips during start, it fails when needed most.

RE: Instantaneous Trip => Rule out mechanical causes

electricpete -
Based on your experience here & the criticality of the application, I would strongly suggest that you increase the instantaneous setting to 1.7x locked rotor.  What you gain in terms of certainty of successful starting will far outweigh the increase in clearing time for actual faults.  Also, installation of a microprocessor relay could be considered - if the cost is justifiable on the basis of security of operation and information available.
 
Of course, you need to look carefully at the effect on coordination with upstream relays.  Confirm that the motor cable is still adequately protected with the higher setting (this should not be a real concern, but needs to be checked).

RE: Instantaneous Trip => Rule out mechanical causes

(OP)
Thanks peterb. You give me confidence that I have assessed the situation correctly. First on the mechanical effects, now on the setpoint change. I have recommended a setpoint increase.  There are still some folks that are skeptical of that recommendation and reluctant to proceed for various reasons. We're going to double-check a few facts and do one more motor check.

RE: Instantaneous Trip => Rule out mechanical causes

Interesting problem, electricpete, I hope you will keep us informed.  My first thoughts are that the analysis here ruling out mechanical causes are quite logical.  Ruling out the trip relay as a cause was a good step too.  My second thoughts however, concern the instaneous trip and inverse time functions.  Are you sure this curve is limited to less than 0.1 seconds?  With the motor checking out ok, something is different here, and the only differences you have pointed out are the supply, and pump loading.  If you were already on the edge of your locked rotor curve vs. trip settings for example, I would not be very confident that no mechanical loading problems could have put you over your trip curve for time periods in the tenths of seconds.  I would not absolutely rule it out without monitoring the motor starting currents.  

RE: Instantaneous Trip => Rule out mechanical causes

Suggestion: Please, would you provide more information about the motor control and power supply quality.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close