Yay, Masonry Veneer House
XR250
I don't do a lot of these any more as siding seems to be in-vogue around here. This house has 3 5/8" limestone veneer (44 PSF). How do y'all handle the situations where the lower roofs abut the 2-story portion? My goto has been to carry the veneer on angle bearing on a triple rafter (per the IRC) but I go further and add a pony wall under the rafter that transfers down to a stout beam or to the foundation elements. I then specify vertical control joints in the masonry where it transitions from wood to masonry support.
The Arch. wants the masonry to go all the way thru with weeps and flashing above the roof lines (I don't know why). I am trying to honor that. Construction sequencing and cost are apparently not issues on this project so no need to consider that.
What ever solution has to provide:
1) Vertical support of the masonry
2) Lateral shear of the lower roof
3) Longitudinal forces in the lower roof
4) Forces from the cantilevered diaphragms at the porches.
I am not a fan of lagging an angle into the gable end studs or to blocking between the studs as this is never done acceptably in my experience.
We've been using a variation of the lag screw into blocking detail. We double up the studs and 'let-in' notch a continuous 2x8 to lag the angle to. I've not heard any complaints but my suspicion is that the 'let in' part gets missed or ignored. I'd be interested to see if there are better/easier options out there as well
Maybe I'm misunderstanding, but a brick veneer wall shouldn't be loadbearing. It can transfer wind loads to the backing, but it shouldn't be a part of the roof support system. Can you transition to a loadbearing block wall beneath the limestone veneer that runs to a support on the foundation? Or can you bring the veneer wall down to a steel angle or beam that is horizontal that is then supported by steel columns (your "pony wall detail)? While the flashing will break bond, I'm not sure that has an impact on the veneer support. I don't know if it would help, but BIA Tech Note 28 on brick veneer/wood studs discusses brick support: https://www.gobrick.com/media/file/28-brick-veneer-wood-stud-walls.pdf.
Interesting. It's like they want to make it look like it's an addition...
If you carry it to the foundation, that's easy. Done.
For additions to veneer buildings, I've specified brackets that get attached to the structural wall behind at some spacing, and then attach a ledger to it. Contractors hate it because they have to remove brick around them, but if they are installed from the start it wouldn't be too bad. It can be a pair of steel plates with a piece of HSS between them. Bolt it to the wall, and then bolt the ledger to it. There are companies that produce similar products for deck ledgers (not the Simpson product you love soooo much...). Here's one that uses a wide flange - neat idea... DeckStruc
Worst case, you can use tension ties?
If you go with the brackets, make sure it's designed so your chords align with a bracket (maybe a beefed up bracket?) that can handle the reaction.
Yup, thought about using these or something similar.... Probably easier to get something fabbed up locally though.
Thanks for the advice.
Ok, how crazy is this? The building science consultant on the job as specified 1/2" plywood on top of all the ceiling joists as an "air barrier". Good for me as that is now my diaphragm for the lower story.. Ironically, this same consultant used to say painted sheetrock is a fine air barrier (which I don't see how it is not). Now the tune has changed. That is what I dislike about building science. They change their mind on stuff every few years.
Alao, should I attach the last rafter or let it go?
If you attach it won't you be loading the masonry veneer with snow / roof LL since it'll be much stiffer than the rafter in bending? In scheme of life probably not a big deal either way, but strictly speaking we're not supposed to load those guys. I'd probably leave it unattached. If you're worried about differential deflection wreaking havoc on your roof flashings, you could double or triple the rafter to reduce the deflection to something (hopefully) small.
BTW if you've calibrated your building science consultant as a reasonably intelligent person, I imagine there is a communication issue more than their opinion changing constantly. Drywall has been used as an air barrier for some time (see here) and any solid material will do the same (see here). The issue, as always, is at the joints, transitions and penetrations. Even typical drywall install (solid material with taped joints) would not be classified as an "Airtight Drywall Approach" for instance; you need gobs of sealant everywhere (see here). There's also the issue of what side of the assembly you want your air barrier on and it's possible they meant something more climate specific.
My plan was not to use the masonry for support - rather try to support the wood framing with wood framing while allowing the masonry to support itself.
He is well respected but also thought of as kind of kooky. Not sure how air is getting thru latex paint and I can't imagine them doing a better job with sealing OSB. It is the same climate as he has always worked in. Also, IMHO, all this "make houses airtight then use an ERV to manage the air changes" is kind of ridiculous. None of this will ever pay for itself in energy savings once you add in the additional upfront costs of the equipment and maintenance. Also, what happens when you run your dryer and chef's style range hood simultaneously?