Dear Mr. Mbrooke
Q. " What X/R ratios are UL listed MCBs tested to? And what do IEC standards require? I can't find any X/R listed for 15-800amp molded case circuit breakers".
A1. In the IEC world, LV Miniature circuit-breaker (MCB) standard is IEC 60898-1.
A1.1 Reference IEC 60898-1:2003-07 states:
i) Test current 4.5-6kA , power-factor range 0.65-0.70,
ii) Test current 6-10kA , power-factor range 0.45-0.50,
iii) Test current 10-25kA , power-factor range 0.2-0.25.
A2. In the IEC world, LV Moulded-case circuit-breaker (MCCB) standard is IEC 60947-2.
A2.1 Reference IEC 60947-2: 2003 states:
i) Test current 10-20kA , power-factor 0.3,
ii) Test current 20-50kA , power-factor 0.25,
iii) Test current >50kA , power-factor 0.2.
A3. BTW Numerous parts of UL 508 had been harmonized with the IEC Standards IEC 60947, listed as (e.g. UL60947-xyz/IEC 60947-xyz) for about a decade. ALL current tests to UL Standards Shall be tested to UL60947-xyz/IEC60947-xyz. Bye bye to UL508.
Che Kuan Yau (Singapore)