Yes, there can be conditions, generally close to generators or the wye side of delta-wye (grounded) transformers, where the SLG fault will produce more current than a 3-phase fault. If the 3-phase fault is balanced, there is no current to ground and there will be no difference in the fault between a 3-phase fault and a 3-phase to ground fault.