I have done several of these types of structures. Expect to use 2x6 stud walls (with several floors with double studs). I have never found code preventing any height of wood structure with the proper engineering(other than fire code restrictions). One of the Structures I did was a four story building with a mezzanine (making it a 4 1/2 story building) on top of a parking garage.
You are required to do a shrinkage calc. I am using the UBC 97 and the Code doesn't require you do anything with it(other than be aware of it in your design), but I would suggest sending the floor to floor and total drift to anyone doing mechanical.
Also make sure your architect knows that brick veneer will require steel lintels and the proper interval (I think it's 35 feet but I'm not sure of the top of my head) unless they use "lick and stick" brick. If you do use brick remeber it will grow over time. So if you are in a specially dry region the differentail can be large. You have to a lot calculations you can usually just assume in shorte would structures. As a rule of thumb, if you think you can analyze it, then do it.
I normally don't go below 4" spacing on plywood assemblies just to be safe about wood splitting. If you use double studs at all floors(K.I.S.S.), I will go all the way down to 2" spacing(you'll need it to take up the wind forces). I also detail the lap conditions for plywood shear walls (you don't want framers messing this up with tight spacings).
Also, don't let the architect give you too many diaphragm irregularities, like dropped corridors. Your going to need every advantage you can get.
Given the Size of the these buildings, They are usually type III construction, so do what you can to stay out of steel, especially in the walls(fire detailing steel in wood walls is a nightmare). 2x6 walls aren't to bad, but depending on how things stack you may not get a 2x6 wall all the time. I have found that using beam grade PSLs can be analyzed to provide equivelant values to steel.
Don't forget that Siesmic forces can control in the long direction of buildings even in lower siesmic Zones. Expect to do a complete diaphragm analysis too.