Hi KootK , I will be happy to post or send drawings. Is there a limit on allowed size at this site?
Probably there will be 2-cross-ties for a 50 foot long wall, so it will not be all diaphragm transfer. Also, it may end up with partially supported ridge. Also, it is trickier as the 'gable ends' are really 4: 12 sloped roof planes. Rectangular pyramid, with 4:12 pitched roof planes, with partial ridge along long axis.
As far as I can tell the tricks are:
--adequate chord nailing at splices... looks to be about 50- 10d common at any splice, might make sense to add LSTA12 or LSTA18 at splices, exterior side of top plate
--adequate nailing at hips--- LVL and PSL can't be used (unless blocked, see below) as nail spacing is a minimum 3" OC for PSL and LVL top edges... so DF and probably minimum 3x lumber or blocking, parallel and nailed to hip. I like the idea of shaped 2x blocking, as the top edge can be ripped so sheathing fits flat to block top.
-- The hips act as collectors. It is probably reasonable to assume that collector-force from the long-wall-diaphragms can be transferred to the end-walls thru to the sloped end-wall-roof diaphragms, if it is designed for required capacity; i.e. collector force transfer and shear capacity needs to be adequate.
-- it might make sense to add wall-corner-straps as the calculated force without-transfer-of-diaphragm-shear-to-'Gable"-end-walls (6000lbs tension, no diaphragm transfer) (hips are pushing corner apart). Wrapping strap around corner is a bit questionable as wood might compress under straps, so there might be steel plates at the corners, under the straps, or angle iron at the corners, under the straps. Corners would have to be slightly rounded so as not to over stress (cut strap).
Also (without complete diaphragm transfer) the hips will be pushing out at the corners (6000lbs no diaphragm transfer) , so the hip has to have enough bearing at the corner so as not to exceed compressive strength of hip or top plates.
The above (other than top-chord splicing) seems like it becomes safety factor, or redundancy, if one is confident of transfer of shear thru diaphragms. So... I would be working with 4000 lbs at corners is probably adequate and safe.
Diaphragms are designed Dead + Live for 1.15/1.6 (ratio of Cd.s) times table values for allowable shear for diaphragms.
I would be happy to hear any other ideas you might have.