Wood question here, looking for some input. I've been asked to determine the likely cause of failure of a wood header:
- Header was a (3)-2x10 that was sparsely through bolted
- Header was in a crawlspace and supported a center bearing wall on a two story apt. house.
- The header was supported on steel pipe columns @ 5'-0" o.c., 20'-0" joists on each side of the header were top bearing on the header
- Each pipe column had a 4"x6" bearing plate on top, lag screws through the bearing plate into underside of header
The header was already removed by the time I inspected it so I didn't see the in-situ condition. However, it was still on site and the problems are pretty evident. There is significant warping of the header. The outer plies are curling outward, and the overall 3x header is twisted. There is also crushing failure at all post locations. In some instances there is up to a 3/4" deep pocket in the header where the bearing plate was located.
Based on some rough calcs it seems like this would have seen about 550psi perp to the grain (bearing). That is high, but I doubt this ever saw a design load - especially at every post location over 80ft. of length. Most likely it saw much less than this. Would you expect to see that much crushing at say the... 300psi or 400psi range? (I don't know the species, this is in the Northeast)
I'm also trying to figure out the twisting. Is this likely the result of some differential moisture issue? Green lumber that was bolted together and then warped as it dried? Or is it related to the crushing? Obviously not looking for anything definitive here, just looking for some opinions. See attached pics.
- Header was a (3)-2x10 that was sparsely through bolted
- Header was in a crawlspace and supported a center bearing wall on a two story apt. house.
- The header was supported on steel pipe columns @ 5'-0" o.c., 20'-0" joists on each side of the header were top bearing on the header
- Each pipe column had a 4"x6" bearing plate on top, lag screws through the bearing plate into underside of header
The header was already removed by the time I inspected it so I didn't see the in-situ condition. However, it was still on site and the problems are pretty evident. There is significant warping of the header. The outer plies are curling outward, and the overall 3x header is twisted. There is also crushing failure at all post locations. In some instances there is up to a 3/4" deep pocket in the header where the bearing plate was located.
Based on some rough calcs it seems like this would have seen about 550psi perp to the grain (bearing). That is high, but I doubt this ever saw a design load - especially at every post location over 80ft. of length. Most likely it saw much less than this. Would you expect to see that much crushing at say the... 300psi or 400psi range? (I don't know the species, this is in the Northeast)
I'm also trying to figure out the twisting. Is this likely the result of some differential moisture issue? Green lumber that was bolted together and then warped as it dried? Or is it related to the crushing? Obviously not looking for anything definitive here, just looking for some opinions. See attached pics.