I have a horizontal sunshade overhang with 11 Ga perforated steel grating with ¾” square holes on 1” oc. So the open area is about 56%. Obviously I would like to reduce the snow and wind load as much as I could and would like to apply the load to about 50% of the area. Is there anything specific about loads on perforated areas on IBC 06?

I remember working on something similar in City of Chicago (vertical mesh type roof enclosure around a basketball court) and the city engineer wanted something in writing from the mesh manufacturer about wind load on partial surface. Wonder how IBC 06 deals with this.
 
Replies continue below

Recommended for you

What happens when a wet snow "clogs" the mesh. I have never seen a an allowable reduction for this. And I don't think I would take much of one.
 
You can't reduce snow load because snow will bridge across such small openings. I would not reduce wind load either, but I don't use IBC so can't comment on what they say.

BA
 
Could ASCE 7-05 Figure 6-22 be applicable (or adapted) for the wind?

I agree on not reducing the snow load.
 
I recommend considering possible future use. Seems people always decide there's too much breeze or sunshine coming through this thing, lets cover it with something.

I saw a baseball backstop fence blow over after a big advertizing banner was installed on it.
 
Even when wind hits the mesh it burbles(??) and partially clogs it. SO if they say it is 50% open - it may well be dimensionally but not aerodynamically. And 5 years down the road when it gets clogged with dust, leaves, etc - back to square one.!!
 
Agree with the others. Use the full load.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 