abusementpark
Structural
- Dec 23, 2007
- 1,087
See the attached detail of a diagonal wind brace connection in which the gusset plate is directly welded to the column and beam and the beam is connected to the column used a bolted connection. I was recently wondering about the common assumptions regarding the transfer of the vertical component of the brace force to the column.
If you're using the Uniform Force Method (UFM), then some of the load will be transferred directly from the gusset plate to the column and the remainder will be transferred from the gusset plate to beam to the column. The actual force proportions are determined by geometry. However, I was thinking about how AISC has a general statement either prohibiting or limiting how much welds and bolts can be combined to transfer a force in a connection. I believe the concern is differing load-deformation relationships and ductility between the two transfer mechanisms. Wouldn't there be a similar concern in this type of connection? Seems to me like the welded connection of the gusset to the column offers a significantly stiffer path compared to the beam-to-column connection.
Any thoughts?
If you're using the Uniform Force Method (UFM), then some of the load will be transferred directly from the gusset plate to the column and the remainder will be transferred from the gusset plate to beam to the column. The actual force proportions are determined by geometry. However, I was thinking about how AISC has a general statement either prohibiting or limiting how much welds and bolts can be combined to transfer a force in a connection. I believe the concern is differing load-deformation relationships and ductility between the two transfer mechanisms. Wouldn't there be a similar concern in this type of connection? Seems to me like the welded connection of the gusset to the column offers a significantly stiffer path compared to the beam-to-column connection.
Any thoughts?