Sorry Mbrooke, I think there's something I'm missing. I'm very interested in what you are saying, just need a little more help getting there...
For a low side fault on a tapped station (which does not have it's own line protection for the HV line its connected to) you do not want your HV line protections tripping. Now we DO use something called 'line back-up' in our tapped transformer stations, but that's a different topic and I don't want to get distracted. The goal is that any fault on the LV side of the tapped station would be cleared by an element on the low side. The only equipment in a tapped station that would trip a HV line for a fault would be a fault in the transformer. And then only because we do not use high side breakers for tapped stations. I am thinking that we typically work on stations with different configurations? Is that why I am still confused?