Hi cranky108.You may be correct as far as larger machines are concerned. However for smaller machines, below about 1 megawatt, the PF rating at 80% is an industry standard. With the different voltages and excitation schemes that may be used with the same alternator in different applications, the capability curves are not usually a limit.
For instance with just a change in model number the same physical gen-set may be rated at 80KVA/100kW prime power, or 90KVA/110kW standby power.
If that set is rated at 240 Volts, the same set will be rated at 85KVA/70kW at 208 Volts. The dead-rack setting may be trimmed back to 70kW or it may be left at the 80kW. If this is a prime rated set, it will then be capable of outputting 88kW, despite the rating of 85KVA/70kW.
Then we come to excitation. Basic AVR, PMG, load current boost module, saturable PT/CT excitation. These are all rated at 0.8 PF and the capability curves will all be different.
I have probably answered sibeen's comment to some extent.
kW describes the minimum power of the prime mover.
...or maybe even the maximum
I have encountered a couple of sets where this was true. Usually there is a little extra capacity in the prime mover to allow for changing atmospheric conditions and engine aging. In Canada a diesel engine may produce 10% more power on summer fuel than it does on winter fuel.
In some installations, for many years old crankcase oil was disposed of in the fuel supply. This increased the SG and as a result improved the power and fuel economy of the prime mover.
With the new generation engines, the fuel filters are much finer to adequately protect the new generation injectors with a much finer spray. With these the cost of replacing fuel filters is greater than the saving in fuel cost.
Bill
--------------------